    Refrigerant Recovery Question?



    Dear All,

    In refrigeration recovery guides, it is said that DO NOT use push/pull method when the system is heat pump or it has suction accumulator.

    Any body can give a reason for this?

    Thanks
    LANA


    Even Einstein Asked Questions

  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Refrigerant Recovery Question?

    Any ideas?
    Even Einstein Asked Questions

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Refrigerant Recovery Question?

    You should not use the push-pull method if the air conditioning system contains less than 10 pounds of refrigerant, if the system is a heat pump, or if it is a unit with a reversing valve. In addition, if the system has an accumulator between the service ports used in liquid recovery or if the refrigerant system doesn’t allow for the formation of a solid column of liquid, you should not use the push-pull method.
    source
    http://www.phaseoutfacts.org/common+recovery+methods+explained.aspx

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Refrigerant Recovery Question?

    Dear install monkey,

    I have read the same article , my question is WHY?

    Thanks
    Even Einstein Asked Questions

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Refrigerant Recovery Question?

    .

    In push pull recovery you pressurise the system with vapour from
    the recovery machine and that vapour is drawn off the top of the cylinder.
    This then pressurises the system and liquid is pushed / pulled out of the
    system to the lower pressure cylinder.

    That can only happen if the system has liquid and vapour separation.

    If a diverting valve was in place or if a suction accumulator was in place
    they could effect the flow of refrigerant and cause the recovery process
    to be inefficient.

    Traditionally, push pull method is connected to the high side and low side.
    By pushing vapour into the system you encourage liquid out but diverting valves
    and suction accumulators might interfere with that process and prevent the
    passing of the liquid??

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Refrigerant Recovery Question?

    Many Thanks.

    Is this only because the recovery process would not be efficient or would it be dangerous?

    Cheers
    LANA
    Even Einstein Asked Questions

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Refrigerant Recovery Question?

    Quote Originally Posted by lana View Post
    Many Thanks.

    Is this only because the recovery process would not be efficient or would it be dangerous?

    Cheers
    LANA
    I can't see why it would be dangerous as long as the pump was set to
    cut out before it got to a pressure higher than the rating on the AC system.

    But Push - Pull only works when you are pushing liquid out and if the components
    inside a heat pump affect the way liquid is transferred, then it will make the whole
    process very inefficient.

    If liquid gets trapped because all the liquid is somewhere it's not meant to be, that
    could be dangerous because you might think all the liquid is out. If you then connect
    the pump to pull the remaining vapour out, you might get a slug of liquid into your
    pump or worse over you (if you thought all the liquid had gone).

    Seems a remote possibility but for a manufacturer it is still a possibility so one
    that needs to be catered for???

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  8. #8
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Refrigerant Recovery Question?

    Thanks a lot for the explanation.
    Cheers
    LANA
    Even Einstein Asked Questions

  9. #9
    Join Date
    Mar 2008
    Location
    u.k
    Posts
    62
    Rep Power
    17
    Hi there

    I have a question on this ?
    I have to recover 55kg of r410a i recovered about 15 kg of liquid today now vapour is left also the bottles are over heating so i have been putting them in a bucket.
    Its on a vrf so in them instructions i cant use push pull method because of the reversing valves etc.
    Is there another way of faster recovery i remember along time ago there is a method.
    Where you link the several bottles in a row but not sure what that is called or how you do it.
    Any help would be appreciated?
    Cheers ian

  10. #10
    Join Date
    Jul 2014
    Location
    UK
    Age
    54
    Posts
    7
    Rep Power
    0

    Re: Refrigerant Recovery Question?

    Are you using a 50kg recovery cylinder or 5x 10kg ones?

    If your pulling 40kgs of Vapour out I'm afraid its going to be a Long Night!

  11. #11
    Join Date
    Mar 2008
    Location
    u.k
    Posts
    62
    Rep Power
    17
    Hi mate

    Yeh I've got 6 10kg bottle because of access etc.
    But maybe wish i had two large bottles know lol.

    Any ideas ?

    Ian

  12. #12
    Join Date
    Jul 2014
    Location
    UK
    Age
    54
    Posts
    7
    Rep Power
    0

    Re: Refrigerant Recovery Question?

    If Its a newer system they tend to Have "recovery Mode" settings that Open all the Internal Valves for You to help get the Gas out, I Also tend to use 2 Recovery Machines.

    Not Sure what Else to suggest, apart from a Deck chair and a good Book.

    Enjoy!