    Daikin VRV2 L8 fault



    Hi guys
    I have been to a system this week which was not running. I started up and system seemed to run fine but have attended next morning to find L8 fault which I understand to be a compressor issue. I reset again and same result following morning, L8 fault present. when now reset slave condensor runs but nothing on master, compressor starts but then stops.
    ran a test mode and got UF??

    system is as follows
    REYQ14M8W1B MASTER
    REYQ16M8W1B SLAVE

    APPROX 9 INDOOR UNITS

    cant phone technical from site of condensers, is it just a faulty main/inverter compressor??
    any tips appreciated, thanks.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin VRV2 L8 fault

    L8

    Inverter compressor over-current

    Abnormal high pressor increase due to blockage of the refrigerant circuit and others.
    Defective compressor.

    UF

    Mis-match of piping and wiring

    Improper connection indoor/outdoor and outdoor/outdoor units feed wiring
    Last edited by frank; 28-02-2014 at 08:46 AM.

  3. #3
    Join Date
    Jan 2013
    Location
    England
    Posts
    11
    Rep Power
    0

    Re: Daikin VRV2 L8 fault

    REYQ14M8W1B is maste unit which is lowest HP unit, is that ok???

    I have taken off panels to start looking and obviously someone has looked before as all jackets are open. There are 3 motors left to right one (larger) with oil return. I havent dealt with these loads, am I correct that the INV comp is (to the left) connected with oil return and cables from compressor go through to INV board behind main board and connect on X11a??

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin VRV2 L8 fault

    The inverter compressor is normally on the left and, as you say, connects to the inverter pcb.

    Have you carried out an insulation test on the pot/pots.

    Are the F1 F2 cables terminated correctly?

  5. #5
    Join Date
    Oct 2013
    Location
    Turkey
    Age
    33
    Posts
    15
    Rep Power
    0

    Re: Daikin VRV2 L8 fault

    hi, outdoor comp. overload, motor disconnected.

    daikin fault codes