25-02-2014, 07:43 PM #1
Daikin vrv2
Need help pls got a reyq16 master and a 14 slave problem is unit seems to get stuck in defrost think its a 4 way valve problem but not a 100% sure reason it only seems to happen of a Monday morning works fine all week system is controlled ny a I touch any suggestions wud be great.
-
25-02-2014, 08:01 PM #2
Re: Daikin vrv2
u sure it isnt struggling to get to setpoint as its been off all weekend- programme an earlier start on monday morning, any vams onsite- start them up only when staff occupy building
-
25-02-2014, 08:17 PM #3
Re: Daikin vrv2
Forgot to mention it has a fabric setting of 18c over weekend cos building is really poorly insulated I have it timed to come on at 4 on the Monday at 25c but it just dosent come on when I arrive on site both condensors are working but all the hot gas goes straight into the condenser coil. I turn both units off turn back on works great all week have checked schedules in I touch everything is set up correctly just a bit at a loss.
-
25-02-2014, 08:25 PM #4
Re: Daikin vrv2
seems strange its only on a monday- u need daikin service checker on it, leave it connected over the weekend to see whats happening
-
25-02-2014, 08:36 PM #5
Re: Daikin vrv2
Ye tried saying that to the boss but won't pay the money thanks for your surgestions I changed the master pcb board today am hoping it's a software problem fingers crossed. I changed the pcb after reading similar problems worth a shot had a spare board.
-
25-02-2014, 09:24 PM #6
Re: Daikin vrv2
had a tosh super multi- had issues with weak solonoid coils- when its in that mode on monday morning- stick a coil lifter on it- then unplug the coil off the pcb- once stuck a screw driver in a coil as its meant to prevent the coil from burning out- but i nearly burnt down a petrol station- coil melted, insulation on screwdriver melted too
Last edited by install monkey; 25-02-2014 at 09:25 PM. Reason: or alternativly buy a sanyaginoya coil for about 12 quid- not from daikin-
-
25-02-2014, 09:31 PM #7
Daikin2
Help need pls have got a reyq16m master and a 14 slave its controllered by a I touch controller problem is building is poorly insulated so units have a fabric setting to run over weekend at 18c. Monday it starts up at 4 at 25c for staff when they come in but it dosent seem to kick in and when I arrive on site both condensors are running but all the hot gas goes straight into the condensor coil. If I reset the units they work all week no problem but Monday morning same thing happens. Have checked I touch it is all set up correctly. Had a problem with a 4 way valve a few weeks ago but managed to free it. Am at a bit of a loss now and really need a bit of advice as u can imagine its driving me mad.
-
25-02-2014, 09:41 PM #8
Re: Daikin2
Everything is normal then, the hot gas should always go to the condenser coil...
OK, I assume you meant the outdoor coil so,
When you arrive and the hot gas goes to the outdoor coil, is the 4way valve's coil energised or not?
-
25-02-2014, 09:50 PM #9
Re: Daikin2
Sorry it's in heating mode so hot gas should be going to fan coils main 4 way valve is energised but sub 4 way isn't?
-
25-02-2014, 10:04 PM #10
Re: Daikin vrv2
any external BMS connected to your I touch? That will hold the system out on Monday morning regardless of your I touch settings. Might be holding the system off over the weekend as well. Unplug it on Friday afternoon and see what happens.
-
25-02-2014, 10:14 PM #11
Re: Daikin vrv2
Two threads merged.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
25-02-2014, 10:27 PM #12
Re: Daikin vrv2
Thanks for reply defo no external bms might try unplugging I touch don't seem to be getting any closer to solving the problem
-
25-02-2014, 10:38 PM #13
Re: Daikin vrv2
Hmmm, seems odd that your I touch is programmed to come on 4 on Monday morning but doesn't. Any external connection at all? Fire alarm relays that could be dropping power on a weekly test? Had a similar problem in the past when a clever **** spark had wired the indoor units power through a contactor on a time clock.
Last edited by NewmanRef; 25-02-2014 at 10:43 PM.