    Cool HELP Daikin twin split r410. L5 fault



    Hi there I have been installing For many years but have moved over to Maintance , repair so picking up as I go along .
    There is L5 fault which suggest , inverter or compressor. , unit was running after resetting , inverter seamed to be working fine as did compressor , it ramped up steadily in heating to around 10 amps and was working for round hour with no issues but whilst had gauges on it was running over 40 bar , talking to technical the suggested the pressure sensor Was faulty , replaced and run again and was still running over 40 bar .
    Unable to observe for any length of time due to branch shutting and had to leave , can any one help ,, cheers



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: HELP Daikin twin split r410. L5 fault

    have u meggered the pot, usually pot failure- siezing or grounding

  3. #3
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: HELP Daikin twin split r410. L5 fault

    Grubby filters?
    Health and safety first..........unless I'm in a hurry.