    Feb 2014
    India
    40
    5
    Post meggar test under high vacuum
    Can anybody suggest that why we should not do meggar test of a motor under high vacuum?
    4,698
    Re: meggar test under high vacuum
    Because it screws the motor windings.
    Read any of the many previous posts on this forum.
    Unless of course you intend to come up with a new way of doing things?
    3,856
    Two reasons, first without the pressure of refrigerant in the compressor there is little to stop the high voltage used in megger testing jumping across windings and connections inside the motor, this can cause tracks similar to old distributor caps and ignition systems in cars, so when you try to run it later on it burns out the motor. Also i expect the resistance values measured would be inaccurate for the same reason causing you to condemn a good motor.
    manchester
    5,639
    can anybody answer why you would need to or want to megger a pot under a vac?
    Quote Originally Posted by rishab1508 View Post
    Feb 2014
    India
    40
    5
    Thanks for your valuable input..