    system imbalance



    Hi folks again...
    honestly we are tyring to figure out some specific problem which leads me to such questions..So what happens if your system components are not choosen accordingly..meaning that your evap. OR your comp. OR your condenser is oversized or undersized for the particular design condition.....
    thx in advance....



  2. #2
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    254
    Blog Entries
    4
    Rep Power
    20

    Re: system imbalance

    You say that you're trying to figure out a specific problem. What's the problem?

    If your system components are not sized properly many things may happen. I suggest you review the following.

    http://www.hvacrinfo.com/Cope_manuals/AE104_R2.pdf

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: system imbalance

    A refrigeration system is a closely balanced system, anything upsetting that balance will affect the performance and reliability of the system.

    As to your openended question...
    What will happen if I cut this cable?
    As you might guess, just as you need more information in order to answer my question, we need more information to be able to answer yours...


  4. #4
    Join Date
    Apr 2012
    Location
    FL
    Posts
    38
    Rep Power
    0

    Re: system imbalance

    Quote Originally Posted by The Viking View Post
    A refrigeration system is a closely balanced system, anything upsetting that balance will affect the performance and reliability of the system.

    As to your openended question...
    What will happen if I cut this cable?
    As you might guess, just as you need more information in order to answer my question, we need more information to be able to answer yours...

    well we are having flood back problem...we have replaced the TXV and still have some liq. coming back...evap capacity is matching txv but compressor is bigger..so can this phenomena cause such problem??? thx....

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: system imbalance

    So what's the Tx valve on?
    Give us some pressures in system, room or water temps, refrigerant type etc etc.

    If TX valve is sized correctly then either there is no heat transfer due to poor air flow or ice build up or something like that.
    If suction pressure is to low because compressor is to big won't necessarily mean flood back.
    Liquid/suction line heat exchangers are renowned to leak internally as we'll.

  6. #6
    Join Date
    Apr 2012
    Location
    FL
    Posts
    38
    Rep Power
    0

    Re: system imbalance

    Quote Originally Posted by RANGER1 View Post
    So what's the Tx valve on?
    Give us some pressures in system, room or water temps, refrigerant type etc etc.

    If TX valve is sized correctly then either there is no heat transfer due to poor air flow or ice build up or something like that.
    If suction pressure is to low because compressor is to big won't necessarily mean flood back.
    Liquid/suction line heat exchangers are renowned to leak internally as we'll.
    hi there..thx for the reply...
    system runs off R404A with ZF40 K4E copeland scroll compressor. Exp valve is Alco TCLE 600SW40 with solenoid right before it(Alco 200 RB 6T5)
    design conditions are -25C evap / 45C condensation....

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: system imbalance

    .

    Hi bjkmiami.

    We need more information.

    To be able to work out if there is a mismatch we need to know
    far more information.

    How old is the system?
    How long has it ran?
    Has it ever ran correctly?
    When did it start to not work correctly?
    What has changed?

    What is the suction pressure / temperature?
    What is the discharge Pressure / temperature?
    What is the temperature of the air onto the heat exchangers?
    What is the temperature of the air off the heat exchangers?

    Then we may be able to talk about it.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: system imbalance

    How have you determined that it is liquid floodback?

    Is it because the suction line is frosting or do you have zero superheat?

  9. #9
    Join Date
    Apr 2012
    Location
    FL
    Posts
    38
    Rep Power
    0

    Re: system imbalance

    Quote Originally Posted by frank View Post
    How have you determined that it is liquid floodback?

    Is it because the suction line is frosting or do you have zero superheat?
    well we have seen an extensive bubbling inside the crankcase of the compressor with the oil...and this was not during start up!!!!and yes superheat was also lower than what is set on the TXV!!!

  10. #10
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    254
    Blog Entries
    4
    Rep Power
    20

    Re: system imbalance

    Is the oil foaming up and staying that way or does the oil clear up? Do you have a crankcase heater? If so, is it working? How often does the compressor cycle off? What is the temperature of the room that the compressor is in? Perhaps off cycle migration is a problem!

    I would start by answering the questions asked by Rob White. Without the numbers, we are simply speculating.

  11. #11
    Join Date
    Apr 2012
    Location
    FL
    Posts
    38
    Rep Power
    0

    Re: system imbalance

    Quote Originally Posted by passandscore View Post
    Is the oil foaming up and staying that way or does the oil clear up? Do you have a crankcase heater? If so, is it working? How often does the compressor cycle off? What is the temperature of the room that the compressor is in? Perhaps off cycle migration is a problem!

    I would start by answering the questions asked by Rob White. Without the numbers, we are simply speculating.
    well what i saw was bubbling and clearing up afterwards from time to time...and i dont think crankcase heaters work while comp is running and this was not a start up!!!!! the room temp was -20C at the time..
    thx...

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: system imbalance

    The following data would provide a much more accurate picture:

    Evaporator air/water in temperature = ?
    Evaporator air/water out temperature = ?
    Low side saturation temperature = ?
    Suction line temperature = ?

    Condenser air/water in temperature = ?
    Condenser air/water out temperature = ?
    High side saturation temperature = ?
    Liquid line temperature = ?

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: system imbalance

    Quote Originally Posted by bjkmiami View Post
    superheat was also lower than what is set on the TXV!!!
    Seriously? You are not even going to tell us what the superheat was (let alone the saturation and suction line temperatures)?... just that it was lower than the TXV setting?

  14. #14
    Join Date
    Apr 2012
    Location
    FL
    Posts
    38
    Rep Power
    0

    Re: system imbalance

    Quote Originally Posted by Gary View Post
    Seriously? You are not even going to tell us what the superheat was (let alone the saturation and suction line temperatures)?... just that it was lower than the TXV setting?
    hello gary...
    well TXV superheat setting was supposd to be 7K we even increased it to 10K at some point but when we measured at the compressor suction we have seen diferent superheat at diferent times..such as 3K 5K 8K.....Couldnt get to the evaporator since the room was loaded badly but they have another unit running in the same room soo they r OK now soon we ll go there again to check on all those parameters u mentioned!!!
    Suction line temp (lowest -22C highest -15C)
    evap temp -25C
    condensation cycle between 30C to 45C and unfortunately i dont have the other parameter at this moment!!i ll try to get it all next visit..
    and thanks for your time!!!

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: system imbalance

    An oversized compressor will make flooding less likely, not more likely.

    If the TXV has the proper orifice, then the most likely cause of hunting would be insufficient airflow through the evaporator (low heat load). Second most likely would be gross refrigerant overcharge.

    If the superheat at the compressor inlet is lower than the superheat at the evaporator outlet, then liquid refrigerant is somehow entering the suction line (suction/liquid heat exchanger leaking internally?)
    Last edited by Gary; 21-02-2014 at 02:46 PM.

  16. #16
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: system imbalance

    Also might be worth looking at the txv feeler bulb for good thermal contact with suction line and in correct position and insulated.Have seen hunting caused by loose feeler bulbs.