    Evaporator Design-Air Source Heat Pump for water heating



    Dear Technocrats,
    I am designing air source heat pump for water heating for Indian conditions
    As a first step, the evaporator is designed. While designing, I have considered two ambient conditions, delta T across evaporator is 46.4 deg. F (8 deg.C.) and R.H. 25%
    The inputs and output calculations are attached.
    Kindly guide me to design it perfectly.
    How much delta T should be designed for getting optimum COP?
    If you face any problem whie reading below calculations, I have attached the same as an attachment.

    Evaporator Design

    Sr. No. Parameters Units Case 1 Case 2
    a Input
    1 Inlet Air Temp deg. F 89.6 68
    2 Outlet Air temp deg. F 75.2 53.6
    3 R.H. at inlet air temp considered 25% 25%
    4 R.H. g/m3 33.83 17.3
    kg/m3 0.03383 0.0173
    5 Refrigerant type R 22 R22
    6 Heat Load Kw 20.15 20.15
    7 Air Flow CFM 3431 3711
    m3/hr 5830 6305
    8 LMTD deg. F 68.97 46.67
    9 Tube Material Cu Cu
    b Output
    1 No. of tubes nos 120 180
    2 Tube length mtr 1.2 1.2
    3 Tube OD mm 12.7 12.7
    4 Tube ID nos 8.5 8.5
    5 No.of Fins/inch nos 13 13
    6 No. of rows nos 3 3
    7 No. of passes nos 14 14
    Attached Files Attached Files



  2. #2
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Evaporator Design-Air Source Heat Pump for water heating

    Hi Anup,
    It's very good to share your design with us. I want to ask something first and then maybe I can say something.
    What's your design standard? refrigerant side and air side. I mean ,what about te tc,superheat and subcool,these one decide the COP.
    is there any standard for air source hp in your country?
    I'll make some calculation later

    good luck

    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

  3. #3
    Join Date
    Sep 2005
    Location
    India
    Age
    49
    Posts
    30
    Rep Power
    0

    Re: Evaporator Design-Air Source Heat Pump for water heating

    Dear LC,
    Thanks for your reply.
    I suppose te is evaporating temp and tc condensing temp. If so, then
    Te - 44.96 F
    Tc - 129.2 F
    We are not going for superheating as well as subcooling temp
    Regards
    Anup

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Evaporator Design-Air Source Heat Pump for water heating

    Quote Originally Posted by anup
    Te - 44.96 F
    Tc - 129.2 F
    You lucky guy. Still, somebody wants air to water heat pump in europe.... asking for high COP....

  5. #5
    Join Date
    Sep 2005
    Location
    India
    Age
    49
    Posts
    30
    Rep Power
    0

    Re: Evaporator Design-Air Source Heat Pump for water heating

    In India, there is no standard for air source heat pump. Infact I would appreciate, if our friends mail me the standards for air source heat pump, which I can lobby with the government. As on today, there is no player in India in air source heat pump

  6. #6
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Evaporator Design-Air Source Heat Pump for water heating

    Air source heat pump design condition is : te=2C and tc=50C in our place. Maybe India's ambient temp is different. How about the summer weather in india? Per Q=KF(LMTD),what's your K and F? If possible,pls lower the condenser temp,which help to increase COP.
    BTW,your terminal is by air or water?

    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  7. #7
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Evaporator Design-Air Source Heat Pump for water heating

    You design the heat pump only for water heating? I refer to your title again.
    We are not going for superheating as well as subcooling temp
    Why ? pls explain

    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Evaporator Design-Air Source Heat Pump for water heating

    If Europe, air source heat pumps are installed in countries where the ambient can be as cold as -5°C (or colder, but it won't work). In that case evaporating temperature can be -12°C.
    In a heat pump, Te is uncontrolled, and is slave of warm water thermoregulation probe, until either it doesn't produce any more warmth than it absorbs for defrosting or it stops by low pressure cut out.
    But India is a whole different story.

Similar Threads

  1. dual source heat pump
    By Lc_shi in forum New Technologies
    Replies: 29
    Last Post: 12-08-2010, 02:24 AM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  4. air source heat pump
    By Lc_shi in forum New Technologies
    Replies: 12
    Last Post: 14-07-2005, 03:55 PM
  5. Mcquay water source heat pump
    By bernie in forum Air Conditioning
    Replies: 2
    Last Post: 10-02-2003, 01:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •