Results 1 to 2 of 2
    Nov 2012
    33
    4
    Chilled Systems Advice/Calculations
    I have a few questions regarding a chilled water system.
    How can I determine the Cooling Capacity required for a room? (Data Centre) In tons.
    Also, how can I determine the optimum flow of water across the evaporator in the room? is there a set water flow/fan speed calculation or graph.
    The temperature difference between chilled water temperature at chiller and the 'in room' evaportator temperature? for example for a AC system its about 10K difference - is that the same with chilled water systems?
    Any information would be greatly appreciated - thanks
    Oct 2001
    Nottingham UK
    5,667
    Re: Chilled Systems Advice/Calculations
    You need to calculate the heat gains (both sensible and latent) of the following:
    Equipment
    Building fabric (solar and transmitted)
    Infiltration
    Ventilation
    Occupancy
    Lighting
    1 Ton Refrigeration is equal to approximately 3.5kW
    The flow through the evaporator will be derived from the formula Q = m c dt
    Where
    Q = Cooling duty (kW)
    m = Mass flow of water
    c = specific heat capacity of the water in kj/kg (4.19 for water)
    dt = the temperature difference of the water through the evaporator (entering/leaving)
    Your required air volume for the total cooling duty will be derived from the formula
    Q = kW x SHR/(t1 - t2) x p
    Where
    Q = Air volume in m3/s
    kW = your total cooling duty
    SHR = sensible heat ratio (Sensible load/sensible load + latent load)
    t1 - t2 = air on/air off temps of evaporator
    p = density of air
    Normal chilled water flow temps for air conditioning are +6C flow, +12C return