Refrigerant quantity&capacity relation
Hi all,
does anyone have a table that shows the capacities of a given refrigerant per kg??
for example R134a -10 to -5C evap temp for 1kW 1-1,5kg refrigerant!!!!
thx alot...
-
18-02-2014, 04:26 PM #2
Re: Refrigerant quantity&capacity relation
What makes you think there is a relationship between quantity and capacity?
-
19-02-2014, 08:11 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Refrigerant quantity&capacity relation
Only relation with capacity is mass flow of refrigerant!
Mass flow is defined with compressor displacement and refrigerant temperature/pressure.Last edited by nike123; 19-02-2014 at 08:13 AM.
-
19-02-2014, 08:49 AM #4
Re: Refrigerant quantity&capacity relation
well i dont have any solid evidence to prove it but one of my buddies in the field said so. so i was trying to get idea of you folks as well...
thx
-
19-02-2014, 03:50 PM #5
Re: Refrigerant quantity&capacity relation
The true answer is that it has no relation what so ever.
Just imagine that you connect a cylinder with 10kG of refrigerant to the system... Would it automatically increase the system's capacity???