    Refrigerant quantity&capacity relation



    Hi all,
    does anyone have a table that shows the capacities of a given refrigerant per kg??
    for example R134a -10 to -5C evap temp for 1kW 1-1,5kg refrigerant!!!!
    thx alot...



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Refrigerant quantity&capacity relation

    What makes you think there is a relationship between quantity and capacity?

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Refrigerant quantity&capacity relation

    Only relation with capacity is mass flow of refrigerant!
    Mass flow is defined with compressor displacement and refrigerant temperature/pressure.
    Last edited by nike123; 19-02-2014 at 08:13 AM.

  4. #4
    Join Date
    Apr 2012
    Location
    FL
    Posts
    38
    Rep Power
    0

    Re: Refrigerant quantity&capacity relation

    well i dont have any solid evidence to prove it but one of my buddies in the field said so. so i was trying to get idea of you folks as well...
    thx

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Refrigerant quantity&capacity relation

    The true answer is that it has no relation what so ever.

    Just imagine that you connect a cylinder with 10kG of refrigerant to the system... Would it automatically increase the system's capacity???