    Basic coil on a contactor



    Morning,

    I'm new'ish to the trade but am fully qualified in AC and Refrigeration the only aspect of the trade that I'm still learning about is the electrical side of certain things.

    Please see attached photo!

    It's from a Toshiba 3 pipe super multi.

    It's off at the minute under an Ad alarm. Basically Ad relates to 3 things which it could be. 1- HP 2- O/L on contactor 3- over heat of compressor.

    It's not 2 as I've checked.

    My question is -image.jpg on the coil of the contactor A1/A2 which way does the current flow to power the coil? Does it flow up through A2 first, then through the loop (yellow) or up through 95 and through A1 first?

    Thank you for any help



  2. #2
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: Basic coil on a contactor

    Power is coming from terminal L2 and supplies voltage to the pink wire that is connect to A1. Current flows through A1 and A2 is being use as the common point.

  3. #3
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Basic coil on a contactor

    I think it's worth mentioning that ergonomically & logically you would expect power to 'follow the numbers', as contractor coils are not polarity sensitive, you often find they have been wired from A2 to A1. Please don't assume that because this machine is A1-A2, all machines & switch boards are.
    Apologies if you're now rolling your eyes & shouting "I knew that!" at your screen.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Basic coil on a contactor

    terminal 95,96 is a switch that will open circuit the contactor coil in an overload condition- preferably run though it with a1 wiring (live to coil) as opposed to using a2- neutral