    Henry Oil separator plugged



    I have a 2 Henry oil separators on a Hill Phoenix rack that are collecting all the oil and not supplying it back to the reservoir for distribution to my regulators. Its a S-5203. I figured out the problem. Now I need to learn my best approach of repair. I have to travel an hour or better back in the sticks to this place and the closet place for any parts is the same distance. I like to go prepared. I have never service an oil separator before. I have a internal drawing of this and know how it works. I am thinking my outlet is plugged or my float has malfunctioned. Any friendly advice is much appreciated. Thanks in advance



  2. #2
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Henry Oil separator plugged

    Make sure first there isnt a blocked oil filter between seperator and resevoir or closed valve on resevoir .If not just isolate seperator ,degas and open gently with a big container under for the oil inside. Give it a good clean and check float moving freely,blow nitrogen through to clear out tube and reassemble.Change oil filter and no harm to isolate compressors and clean internal oil filters if present.I have never had to change a seperator float but have come across a few blocked up with dirt

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Henry Oil separator plugged

    Sounds like cleansing it is needed,as the previous poster said would make sure about changing/cleansing all the filters on the system and changing the oil making sure to use the correct type.

  4. #4
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: Henry Oil separator plugged

    Yeah just remember to fully isolate the separator before gently opening, otherwise it gets messy! (Not that I have ever made that mistake ).

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Henry Oil separator plugged

    The reservoir pressure would also require checking.
    If to high or no pressure difference then no flow from oil separator's
    Guessing it should be about 15 to 25 psi higher than maximum suction pressure.

  6. #6
    Join Date
    Jan 2011
    Location
    USA
    Age
    61
    Posts
    23
    Rep Power
    0

    Re: Henry Oil separator plugged

    Thank you all for taking the time to respond. I am hoping my isolation valves still work. I haven't been so lucky on other sections on this rack. I have checked to ensure the reservoir is open. It does have a sporlan drier down stream of it before the regulators. I will go through it and let you know. Thanks

  7. #7
    Join Date
    Sep 2011
    Location
    USA
    Age
    45
    Posts
    85
    Rep Power
    14

    Re: Henry Oil separator plugged

    Is it an an impingement style separator? If so make sure the impingement screen isn't blown out. If it is new separator, if not get a separator float(if it is removable) and change that.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Henry Oil separator plugged

    Check that the sporlan drier is a strainer for oil not your regular liquid line drier.

  9. #9
    Join Date
    Jan 2011
    Location
    USA
    Age
    61
    Posts
    23
    Rep Power
    0

    Re: Henry Oil separator plugged

    Quote Originally Posted by Coorsman777 View Post
    Is it an an impingement style separator? If so make sure the impingement screen isn't blown out. If it is new separator, if not get a separator float(if it is removable) and change that.
    So I am clear, "if the screen is blown out of place" separator is toast? I have two that are plugged or not working. S-5294 and S-5203. They both use the same float. I have read that at the screen the oil drips down and the gas escapes. With out the screen its shot? Thanks for the help.

  10. #10
    Join Date
    Sep 2011
    Location
    USA
    Age
    45
    Posts
    85
    Rep Power
    14

    Re: Henry Oil separator plugged

    Yes if the screen is ripped the separator is toast. The oil passes through opening where it ripped rather than through the screen and does not separate the oil from the refrigerant. This is a common occurance on low temp R-22 systems or very dirty systems. The junk left behind from running high discharge temps and the oil breaking down plugs this screen.

    I just looked up the M#'s you gave and those are helical and no the impingement so that isn't your problem. I would swap the floats. Buy a new one for an easy swap out. Then you can clean the old one up and use it again if you run in to a plugged or dirty float.

    I always carried a clean float on the truck and anytime I did an oil change or had a plugged float i would use the clean float and clean up the one I took out. I probably only purchased 2 new floats in 10 years but probably swapped out about 30 of them.

    Sorry I was a little long winded but hope it helped.

    Snap some pics of the old floats and post them. Curious to see.

  11. #11
    Join Date
    Jan 2011
    Location
    USA
    Age
    61
    Posts
    23
    Rep Power
    0

    Re: Henry Oil separator plugged

    Quote Originally Posted by Coorsman777 View Post
    Yes if the screen is ripped the separator is toast. The oil passes through opening where it ripped rather than through the screen and does not separate the oil from the refrigerant. This is a common occurance on low temp R-22 systems or very dirty systems. The junk left behind from running high discharge temps and the oil breaking down plugs this screen.

    I just looked up the M#'s you gave and those are helical and no the impingement so that isn't your problem. I would swap the floats. Buy a new one for an easy swap out. Then you can clean the old one up and use it again if you run in to a plugged or dirty float.

    I always carried a clean float on the truck and anytime I did an oil change or had a plugged float i would use the clean float and clean up the one I took out. I probably only purchased 2 new floats in 10 years but probably swapped out about 30 of them.

    Sorry I was a little long winded but hope it helped.

    Snap some pics of the old floats and post them. Curious to see.
    I will post some pics and no worries about being long winded. I am the same way- I like a clear picture. Turns out I have about 7 Superior ball valves that don't hold (isolate) I am not really using 7 but at least 3 or 4. I have to pull the gas, all 1000 lb.s. I recommended replacing the ball valves at the same time. They put the repair off till April 1st. So expect a delay on the pics till then. Thank you for your input. I have two new floats on hand for the job. New oil filter and of course driers.