Results 1 to 11 of 11
    Dec 2010
    Toronto, Canada
    1,454
    really cold conditions
    I have a situation where is -50C on the fridge side and I need to transfer the heat/cool to a fan coil but I cannot use glycol as it turns to jello. What is used at these temps for a heat transfer fluid?
    Auckland
    74
    3,357
    37
    Re: really cold conditions
    Hi Mike.
    I believe a product called temper goes down to -55' C and stays fluid.
    Dec 2010
    Toronto, Canada
    1,454
    Thanks Magoo, Found it but not found a supplier in Canada. Europe so far.
    ireland
    1,450
    41
    Would Dowtherm or siltherm work at -50?
    Apr 2008
    Canada
    253
    4
    21
    You may find this helpful.
    Attached Files Attached Files
    Dec 2010
    Toronto, Canada
    1,454
    Yes, thanks...
    Auckland
    74
    3,357
    37
    Hi Mike
    if a small system volume, consider pure alcohol. The non drinkable stuff, highly volatile though.
    northernbeach's Avatar
    northernbeach Guest
    Thanks for sharing it.
    Dec 2010
    Toronto, Canada
    1,454
    We used 55% Dowtherm. works a treat
    Sep 2009
    Iran
    66
    672
    1
    Kerosene ( with out any wax ) is a good for this kind of jobs.
    it is more safe than alcohol.
    Mar 2009
    U.S.A.
    320
    Delimone. Its somewhat corrosive and it likes mineral oil; not flammable and very low viscosity even at these temps.