Hi there
having problems finding a leak on a r410a city multi using OFN. System will hold 32bar over the weekend but will lose 9kg in less than a week when running.
Im aware there is better methods due to the municles being bigger in the OFN than the refrigerant.
Many thanks
-
08-02-2014, 03:22 PM #2
Re: Finding a leak on a R410a city multi
check the bc box
-
08-02-2014, 03:26 PM #3
Re: Finding a leak on a R410a city multi
already checked this, no sign of oil anywhere
-
08-02-2014, 04:32 PM #4
Re: Finding a leak on a R410a city multi
Sounds like you have a leak that only surfaces when the system is running and the pipes are vibrating or expanding/contracting.
A few years back I had the same problem which was finally traced to a nail head that had become lodged inside the pipework (which had been rested on top of it).
It was only when the system was running that the pipes must have slightly vibrated that the leak became visible.
Can you access or see all of the pipework to do a visual check?The difference between genius and stupidity is that genius has its limits.
Marc
-
09-02-2014, 07:07 AM #5
Re: Finding a leak on a R410a city multi
thanks Marc starting too look like is the problem, have you used hydrogen are helium for leak testing and if so what sort of pressures should I be looking too test too
-
09-02-2014, 07:18 AM #6
Re: Finding a leak on a R410a city multi
The difference between genius and stupidity is that genius has its limits.
Marc
-
09-02-2014, 09:28 AM #7
Re: Finding a leak on a R410a city multi
I never did track down the waitrose guy...
http://www.refrigeration-engineer.co...p?38520-Scents
-
09-02-2014, 09:36 PM #8
Re: Finding a leak on a R410a city multi
I had the same problem it was the expansion valve inside a cassette
-
10-02-2014, 06:46 PM #9
Re: Finding a leak on a R410a city multi
Try uv dye
-
10-02-2014, 08:58 PM #10