    high suction pressure



    Hello,

    I'm doing commisioining duct-split unit (DX system),
    detailed outdoor-unit with a scroll compressor copeland ZR72KC-TFD (I max 12A)
    R407C charge, indoor-unit with cooling coil capacity 14.3kw with danfoss expansion
    TGEX-6TR-20kw (P.N.067N2236)
    T room control setting at 24C.

    after vacuumizing and charging R407C, start-up and running the unit,
    after 12 hours running,
    T room is still too high at 25-27C
    Suction pressure = 80PSiG and liquid pressure = 270 PSiG
    the compressor I run = 8 Ampere
    what's about wrong with this unit??

    I'm confused why the suction pressure can be high (80 psig)
    My last bit of waste refrigerant (from liquid line), and then
    pressure turns into P suct = 80PsiG P liquid = 255 psig

    Please opinion or input to have experienced the above case.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: high suction pressure

    Evaporator air in temperature = ?
    Evaporator air out temperature = ?
    Low side saturation temperature = ?
    Suction line temperature = ?

    Condenser air in temperature = ?
    Condenser air out temperature = ?
    High side saturation temperature = ?
    Liquid line temperature = ?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: high suction pressure

    High load on system or unit undersized plus we need all the information that Gary detailed.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2014
    Location
    indonesia
    Posts
    11
    Rep Power
    0

    Re: high suction pressure

    Garry and Brian,

    Noted.
    Thank you for the advice

  5. #5
    Join Date
    Aug 2010
    Location
    England
    Age
    53
    Posts
    77
    Rep Power
    16

    Re: high suction pressure

    Quote Originally Posted by apandi View Post
    Hello,

    I'm doing commisioining duct-split unit (DX system),
    detailed outdoor-unit with a scroll compressor copeland ZR72KC-TFD (I max 12A)
    R407C charge, indoor-unit with cooling coil capacity 14.3kw with danfoss expansion
    TGEX-6TR-20kw (P.N.067N2236)
    T room control setting at 24C.

    after vacuumizing and charging R407C, start-up and running the unit,
    after 12 hours running,
    T room is still too high at 25-27C
    Suction pressure = 80PSiG and liquid pressure = 270 PSiG
    the compressor I run = 8 Ampere
    what's about wrong with this unit??

    I'm confused why the suction pressure can be high (80 psig)
    My last bit of waste refrigerant (from liquid line), and then
    pressure turns into P suct = 80PsiG P liquid = 255 psig

    Please opinion or input to have experienced the above case.
    A suction pressure of 80 psi isn't unremarkable with an air on of 27C? Set the head pressure controller to maintain 265 psi and add gas until the liquid line measure about 35 C, this will give you 9K subcooling and you shouldn't be far wrong at this point. When the room temp gets to 22 then check your superheat and adjust as required. 4 - 10 will probably be ok for most applications?

    This is the best I can come up with with the info at hand?

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: high suction pressure

    Did you liquid charge the system.