    Post Toshiba VRF H07 Alarm Code



    Good morning all, My name is Engr Ikedi, Please am experiencing H07 alarm code on toshiba VRF SMMS model.
    I have pump down the unit and top two liters of oil to the unit but still yet the alarm code is still occurring. I have also changed TK1 and TK2 sensor and the alarm is not yet cleared. Please I need somebody who have come across the H07 alarm code and solved the problem to help me out. please I need urgent respond.
    Thanks for your understanding and co-operation.



  2. #2
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Toshiba VRF H07 Alarm Code

    <All outdoor units in
    corresponding line to be
    checked>
    • Check balance pipe
    service valve to confirm full
    opening.
    • Check connection and
    installation of TK1, TK2,
    TK3, TK4, and TK5
    sensors.
    • Check resistance
    characteristics of TK1,
    TK2, TK3, TK4, and TK5
    sensors.
    • Check for gas or oil leak in
    same line.
    • Check for refrigerant
    entrapment inside
    compressor casing.
    • Check SV3A, SV3B,
    SV3C, SV3D, SV3E, and
    SV3F valves for defect.
    • Check oil return circuit of
    oil separator for clogging.
    • Check oil equalizing circuit
    for clogging.

    Toshiba makes oil return more often then others VRF brands.
    Check oil return from oil separator and liquid separator. Check compressor heaters. If there are no leaks in the system, you will need to merge 2 liters of oil))
    Last edited by RusBuka; 05-02-2014 at 11:15 AM.

  3. #3
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: Toshiba VRF H07 Alarm Code

    Quote Originally Posted by Ikedi View Post
    Good morning all, My name is Engr Ikedi, Please am experiencing H07 alarm code on toshiba VRF SMMS model.
    I have pump down the unit and top two liters of oil to the unit but still yet the alarm code is still occurring. I have also changed TK1 and TK2 sensor and the alarm is not yet cleared. Please I need somebody who have come across the H07 alarm code and solved the problem to help me out. please I need urgent respond.
    Thanks for your understanding and co-operation.
    Is the system in module format (numerous condensers linked together) ? if so has the oil balancing line been installed? it can take ages for the fault to show its self if it has not been installed.

  4. #4
    Join Date
    Feb 2014
    Location
    Nigeria
    Age
    37
    Posts
    3
    Rep Power
    0

    Re: Toshiba VRF H07 Alarm Code

    The system is module format and the oil balancing line have been installed. The system is over 6 years. please advice me more

  5. #5
    Join Date
    Oct 2013
    Location
    Turkey
    Age
    33
    Posts
    15
    Rep Power
    0

    Re: Toshiba VRF H07 Alarm Code

    protection for oil level drop detection.

    you can see more.

  6. #6
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: Toshiba VRF H07 Alarm Code

    Quote Originally Posted by Ikedi View Post
    The system is module format and the oil balancing line have been installed. The system is over 6 years. please advice me more
    Are there any oil traps? are the modular condenser joints installed correctly? is the oil sensor defective? are the module condenser installed at the same level (no more than a 0.5m height difference)? or simply is there a oil/refrigerant leak?

  7. #7
    Join Date
    Oct 2013
    Location
    Turkey
    Age
    33
    Posts
    15
    Rep Power
    0

    Re: Toshiba VRF H07 Alarm Code

    hi, Check item
    • Check full opening of service valve of balance pipe.
    • Check connection and installation of TK1, TK2, TK3, and TK4
    sensors.
    • Check characteristics of TK1, TK2, TK3, and TK4 resistance
    values.
    • Check gas leak and oil leak in the same line.
    • Check refrigerant stagnation in compressor.
    • Check error of SV3A, SV3B, SV3C, SV3D, and SV3E valves.
    • Check clogging of oil separator oil return circuit.
    • Check clogging of oil-equation circuit

    see more..