Results 1 to 2 of 2
Thread: R404A to R407F
    Jan 2013
    Turkey
    3
    Question R404A to R407F
    Hello everybody ,
    I need information about R407F performance. I googled but not convinced. So what are you thinking about R407F ?
    I have a Plug-in freezer with 3 doors and 2 doors. They uses R404a but i need to change them to R407F , they have Tecumseh hermetic comps.
    Basicly, Can i charge R407F to Tecumseh comp which uses R404A ?
    What must be change in the system?
    3,853
    Re: R404A to R407F
    The compressor would probably be ok as R407F is similar to R22/R404A
    The likely problem is going to be the expansion device, if the system has a capillary tube it will be too high a flow for R407F and will need changing, if it has a thermostatic expansion valve, it will either need a new orifice or replacement to one suited to R22.
    Best to stick with R404A, or even R507 in my opinion.