    Question R404A to R407F



    Hello everybody ,

    I need information about R407F performance. I googled but not convinced. So what are you thinking about R407F ?
    I have a Plug-in freezer with 3 doors and 2 doors. They uses R404a but i need to change them to R407F , they have Tecumseh hermetic comps.
    Basicly, Can i charge R407F to Tecumseh comp which uses R404A ?
    What must be change in the system?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: R404A to R407F

    The compressor would probably be ok as R407F is similar to R22/R404A

    The likely problem is going to be the expansion device, if the system has a capillary tube it will be too high a flow for R407F and will need changing, if it has a thermostatic expansion valve, it will either need a new orifice or replacement to one suited to R22.

    Best to stick with R404A, or even R507 in my opinion.