what will be the outcome if an 134a expansion valve had been used to a r22 refrigeration system?
thanks!
-
15-03-2006, 09:53 PM #2
Re: 134a expansion valve question
Nice intro.
Why, have you tried this or was the right valve not in stock?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
16-03-2006, 03:57 PM #3
Re: 134a expansion valve question
The outcome would be that compressor woud be unhapy and close to death.
Dont try that,
Renato
-
18-03-2006, 03:06 AM #4
Re: 134a expansion valve question
The valve doesn't really differentiate between refrigerants. But a particular valve will be rated at different tonnages or capacities that are tested by the manufacturer. For example, a 1 ton valve with R22 might become a 1/2 ton valve with R134a. R22 removes a lot more heat as one pound boils, compared to 134a. Thus, a one-ton R22 valve will have a smaller orifice than a one-ton 134a valve. Depending on the particular circumstance, you could likely wind up with an oversized valve, by at least 33%.
But the power head DOES differentiate between refrigerants. And the power head will not exert sufficient pressure to operate correctly. You have a chance of changing powerheads to make the oversized valve work properly, depending upon the valve's original range (for example, you are working with an already-undersized 134a valve), but a small chance of making it work with a 134a powerhead.
Oh! Your original question just came back into mind.
"what will be the outcome if an 134a expansion valve had been used to a r22 refrigeration system?"
You will overfeed liquid to the compressor.Last edited by Dan; 18-03-2006 at 03:09 AM.
Similar Threads
-
Fitting an expansion valve question
By Larry2 in forum Air ConditioningReplies: 20Last Post: 08-04-2008, 04:17 PM -
expansion valve aint cold
By justinworne in forum Trouble ShootingReplies: 6Last Post: 26-07-2006, 10:52 PM -
I want to find detailed files about ALCO zz thermo expansion valve
By brightfu1 in forum FundamentalsReplies: 2Last Post: 07-09-2005, 03:07 PM -
pressure drop between expansion valve and distributor
By aygul in forum Technical SpeculationsReplies: 10Last Post: 22-01-2004, 09:47 AM -
Oversizing EXV electronic expansion valve
By aygul in forum Technical DiscussionsReplies: 5Last Post: 20-11-2003, 01:00 PM