    Charging of the system through the low side.

    Hi Guys,

    Today I was reading the refrigerant handling code of good practice 2007 and it says under the charging of refrigerant .

    All self contained low charge systems are not required to be charged into the low side of the system.

    My worry is that if you cant charge into the low side of the system then how will you charge the system. as high side will have high pressure and gas will not go into the system.

    Please help because i have always charged system on the low side.

    Thanks All help appreciated

  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Charging of the system through the low side.

    .

    Once the system is running you will struggle to charge
    into the high side as you say because of the pressures
    (unless you use a recovery machine to push the refrigerant in).

    But I think what they are saying on the code of good practice
    you are referring to is that most small splits are capable
    of taking liquid in the suction because they tend to be heat pumps
    and will have suction accumulators to protect the comps.

    But you need to know your equipment and different systems work differently.

    In my opinion good practice would keep liquid away from the suction at all costs.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Charging of the system through the low side.

    Also when first charging a system you will be using the vacuum in the system to draw the refrigerant in.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Charging of the system through the low side.

    Small systems you can dump the whole charge in as liquid, so long as you give the system time for the refrigerant to migrate throughout the system before turning it on, so in that case you could dump it all in the high side of a non operational system.
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    May 2012
    Location
    AUSTRALIA
    Age
    34
    Posts
    53
    Rep Power
    12

    Re: Charging of the system through the low side.

    will try dump method this time.

    Thanks a lot guys.