    Capacity Slide problem



    Unable to start the compressor due to the capacity slide value being at 19%, Is there anyway of reducing this so the compressor can be started?



  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Capacity Slide problem

    Can you change the parameter value for minimum start position?

    I often use a instrument signal generator as work around.

  3. #3
    Join Date
    Jan 2014
    Location
    United Kingdom
    Age
    54
    Posts
    26
    Rep Power
    0

    Re: Capacity Slide problem

    iF i get the capacity slide value to read 0% , the compressor will start with a loading of 19% will this be ok

  4. #4
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Capacity Slide problem

    I've seen compressors start at 100%, the lights go pretty dim for a while..
    Last edited by HVACRsaurus; 31-01-2014 at 08:49 AM.

  5. #5
    Join Date
    Jan 2014
    Location
    United Kingdom
    Age
    54
    Posts
    26
    Rep Power
    0

    Re: Capacity Slide problem

    Right thats what i was worried about I can fabricate a 0% but just uncertain of starting the compressor under load

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Capacity Slide problem

    Type of compressor & control system would be helpful to diagnose problem.
    Each brand has its own characteristics etc.
    There must be a reason for it to lose calibration, or a least check possibilities.
    Once you reset 0%, you then have to re-calibrate 100% to get most out of your machine.
    Last edited by RANGER1; 31-01-2014 at 10:27 AM.

  7. #7
    Join Date
    Jan 2014
    Location
    United Kingdom
    Age
    54
    Posts
    26
    Rep Power
    0

    Re: Capacity Slide problem

    There are two compressors , a H.P Compressor and Booster compressor with unisab controllers and a trend IQ151+ CONTROLLER. NH3 system chilling a tunnel at -45

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Capacity Slide problem

    Quote Originally Posted by Markridgway View Post
    Unable to start the compressor due to the capacity slide value being at 19%, Is there anyway of reducing this so the compressor can be started?
    As ranger implies it depends what screws you have.
    I have carefully bled the slide return oil line before now.
    To break the hydraulic lock that can sometimes occur following a unscheduled shutdown.
    It can get a bit smelly and synthetic oils are messy.
    But it works as the slide should then return to its stop under the spring alone.

    Careful mind!
    Grizzly.