Capacity Slide problem
Unable to start the compressor due to the capacity slide value being at 19%, Is there anyway of reducing this so the compressor can be started?
-
30-01-2014, 11:53 PM #2
Re: Capacity Slide problem
Can you change the parameter value for minimum start position?
I often use a instrument signal generator as work around.
-
31-01-2014, 02:15 AM #3
Re: Capacity Slide problem
iF i get the capacity slide value to read 0% , the compressor will start with a loading of 19% will this be ok
-
31-01-2014, 07:04 AM #4
Re: Capacity Slide problem
I've seen compressors start at 100%, the lights go pretty dim for a while..
Last edited by HVACRsaurus; 31-01-2014 at 08:49 AM.
-
31-01-2014, 08:00 AM #5
Re: Capacity Slide problem
Right thats what i was worried about I can fabricate a 0% but just uncertain of starting the compressor under load
-
31-01-2014, 10:18 AM #6
Re: Capacity Slide problem
Type of compressor & control system would be helpful to diagnose problem.
Each brand has its own characteristics etc.
There must be a reason for it to lose calibration, or a least check possibilities.
Once you reset 0%, you then have to re-calibrate 100% to get most out of your machine.Last edited by RANGER1; 31-01-2014 at 10:27 AM.
-
31-01-2014, 06:01 PM #7
Re: Capacity Slide problem
There are two compressors , a H.P Compressor and Booster compressor with unisab controllers and a trend IQ151+ CONTROLLER. NH3 system chilling a tunnel at -45
-
31-01-2014, 08:31 PM #8
Re: Capacity Slide problem
As ranger implies it depends what screws you have.
I have carefully bled the slide return oil line before now.
To break the hydraulic lock that can sometimes occur following a unscheduled shutdown.
It can get a bit smelly and synthetic oils are messy.
But it works as the slide should then return to its stop under the spring alone.
Careful mind!