    Acson fault reset



    Hi can anyone help.
    I have replaced the outdoor sensor on a ducted Acson a.c. after the fault code E3 came up.
    How do I re set the wired remote to restart the unit?



  2. #2
    Join Date
    Jan 2008
    Location
    Spain
    Posts
    14
    Rep Power
    0

    Re: Acson fault reset

    Problem solved. Poor solder joint on internal pcb. No reset required for the wired remote.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Acson fault reset

    Well spotted.