    How to estimate the capacity of a chilled water AHU designed for office comfort



    I have a very old model AHU manufactured by YORK Borg Warner. The name plate of the AHU is missing too.

    Is there a general rule of thumb to estimate the cooling capacity by the surface area of the chilled water coil?

    Or by blower motor horsepower etc?

    Thank you for any input.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: How to estimate the capacity of a chilled water AHU designed for office comfort

    If it is working you can find the duty from the flow rate and the delta t

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: How to estimate the capacity of a chilled water AHU designed for office comfort

    Q = m x Cp x p x DT
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: How to estimate the capacity of a chilled water AHU designed for office comfort

    Can't give you Rep Marc...must spread it around etc lol..

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: How to estimate the capacity of a chilled water AHU designed for office comfort

    Thanks anyway Frank
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: How to estimate the capacity of a chilled water AHU designed for office comfort

    Quote Originally Posted by frank View Post
    If it is working you can find the duty from the flow rate and the delta t
    Chilled water flow rate or Air flow? Delta T of air or water? Tq

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: How to estimate the capacity of a chilled water AHU designed for office comfort

    Airflow (volume) over the coil, air on temps, air off temps.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: How to estimate the capacity of a chilled water AHU designed for office comfort

    Delta T DB will give sensible heat capacity, Delta h will give total heat, probably the water test would be easier
    Q= water flow rate x DT x 4.2kj/Kg ' C

  9. #9
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: How to estimate the capacity of a chilled water AHU designed for office comfort

    for example:

    Air quantity =370CFM
    Temperature of air entering the coil DB = 78F
    " WB = 67F
    Temperature of air leaving the coil DB = 59F
    " WB = 57F
    Enthalpy of air at 67F WB = 31.62 BTU/lb
    Enthalpy of air at 57F WB = 24.48 BTU/lb
    enthalpy deference = 7.14BTU/lb
    capacity = 4.5*370*7.14= 11888 BTU/lb