    Megger a compressor on a City Multi



    Hi all,

    very simple question which I would be grateful if any one could assist or provide the correct advice on the below question -

    when 'Meggering' an hermetic compressor on a Mitsubishi City Multi condenser which setting on my Megger is best suited to check the windings?

    250v
    500v
    1000v

    ?

    Many thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Megger a compressor on a City Multi

    500 typically
    dont forget to disconnect the leads from the inverter board- and make sure ur testing phase to earth

  3. #3
    Join Date
    May 2008
    Location
    Newcastle under Lyme
    Posts
    112
    Rep Power
    17

    Re: Megger a compressor on a City Multi

    Quote Originally Posted by install monkey View Post
    500 typically
    dont forget to disconnect the leads from the inverter board- and make sure ur testing phase to earth
    Will do, much appreciated.

    thanks for the reply.

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Megger a compressor on a City Multi

    Hi Daz.

    Stuff I've read generally says to megger at twice the operating voltage.
    In that case a 3 phase inverter you'd megger at 1kV.

    Still, read a lot of stuff, not sure how much is true but I've not meggered anything to death. Yet...

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Megger a compressor on a City Multi


  6. #6
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Megger a compressor on a City Multi

    Never have used more than 500V as I was taught that 1000V may blow the winding klixons - on comp's where the beads are in the windings.

  7. #7
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Megger a compressor on a City Multi

    nike, thanks your link.more info, good information about meggering.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Megger a compressor on a City Multi

    Last edited by nike123; 27-01-2014 at 09:21 AM.

  9. #9
    Join Date
    May 2008
    Location
    Newcastle under Lyme
    Posts
    112
    Rep Power
    17

    Re: Megger a compressor on a City Multi

    Cheers all for the feedback. - common question really but wanna make sure before I mess up potentially a perfectly good compressor.

  10. #10
    Join Date
    May 2008
    Location
    Newcastle under Lyme
    Posts
    112
    Rep Power
    17

    Re: Megger a compressor on a City Multi

    Compressor tested out okay to be honest. With my Megger set on the 500v range, connected my black lead to the oil equalising line (copper pipe, which I cleaned with emery cloth) my red lead to each terminal U,V&W on each winding it took its time (about 40 secs) I got to >1Mohm. After speaking to Mitsi they suggested a replacement inverter pack. Cheers blokes

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Megger a compressor on a City Multi

    u can test the inverter circuit but pulling the leads off the comp, flick a dip switch on the inverter pcb - not the comms board- test your getting 180v ac on any 2 phases

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Megger a compressor on a City Multi

    For compressors with modern insulation (manufactured after 1975) 100 Mega-ohms is value for pass/fail judgment.
    I would say that your is "mature" for replacement.

    New compressor have insulation resistance more than 10 Giga-ohms at 500V test voltage (OL indication on my megger or out of range, which is 10 Gohm at 500V).
    Check it on new one, you will see.

    1 Mega-ohm or similar mean 10000 times weaker insulation than it was when manufactured. Certainly not good, by my judgment. And, I would say, clear indication that whindings are not in good shape.
    Last edited by nike123; 30-01-2014 at 07:58 AM.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Megger a compressor on a City Multi

    Some insulations in use since 1975 have improved insulating values that may not readily allow leakage current, may have insulation-resistance-testing values near 20,000 megohms (20 gigohms), and may be unacceptable for use if insulation-resistance-testing values are below 100 megohms, regardless of whether or not the windings have surface contaminants.
    http://flic.kr/p/jAZe2W

    http://hpac.com/motors-drives/testing-hvac-motors-0509

    http://www.pearl1.org/standards/Tabl...0Electrica.pdf

    http://www.ewh.ieee.org/cmte/pes/mat...t_May-08R1.pdf
    Last edited by nike123; 29-01-2014 at 07:39 PM.