Results 1 to 13 of 13
26-01-2014, 06:30 PM #1
Megger a compressor on a City Multi
Hi all,
very simple question which I would be grateful if any one could assist or provide the correct advice on the below question -
when 'Meggering' an hermetic compressor on a Mitsubishi City Multi condenser which setting on my Megger is best suited to check the windings?
250v
500v
1000v
Many thanks
26-01-2014, 06:33 PM #2
Re: Megger a compressor on a City Multi
500 typically
dont forget to disconnect the leads from the inverter board- and make sure ur testing phase to earth
26-01-2014, 07:16 PM #3
26-01-2014, 09:12 PM #4
Hi Daz.
Stuff I've read generally says to megger at twice the operating voltage.
In that case a 3 phase inverter you'd megger at 1kV.
Still, read a lot of stuff, not sure how much is true but I've not meggered anything to death. Yet...
Cheers,
26-01-2014, 10:26 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
27-01-2014, 12:30 AM #6
Never have used more than 500V as I was taught that 1000V may blow the winding klixons - on comp's where the beads are in the windings.
27-01-2014, 09:02 AM #7
27-01-2014, 09:17 AM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Here is another thread:
http://www.refrigeration-engineer.co...tion-measuringLast edited by nike123; 27-01-2014 at 09:21 AM.
27-01-2014, 09:45 AM #9
Cheers all for the feedback. - common question really but wanna make sure before I mess up potentially a perfectly good compressor.
27-01-2014, 10:04 AM #10
Compressor tested out okay to be honest. With my Megger set on the 500v range, connected my black lead to the oil equalising line (copper pipe, which I cleaned with emery cloth) my red lead to each terminal U,V&W on each winding it took its time (about 40 secs) I got to >1Mohm. After speaking to Mitsi they suggested a replacement inverter pack. Cheers blokes
27-01-2014, 09:37 PM #11
u can test the inverter circuit but pulling the leads off the comp, flick a dip switch on the inverter pcb - not the comms board- test your getting 180v ac on any 2 phases
29-01-2014, 06:55 PM #12
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
For compressors with modern insulation (manufactured after 1975) 100 Mega-ohms is value for pass/fail judgment.
I would say that your is "mature" for replacement.
New compressor have insulation resistance more than 10 Giga-ohms at 500V test voltage (OL indication on my megger or out of range, which is 10 Gohm at 500V).
Check it on new one, you will see.
1 Mega-ohm or similar mean 10000 times weaker insulation than it was when manufactured. Certainly not good, by my judgment. And, I would say, clear indication that whindings are not in good shape.Last edited by nike123; 30-01-2014 at 07:58 AM.
29-01-2014, 07:18 PM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Some insulations in use since 1975 have improved insulating values that may not readily allow leakage current, may have insulation-resistance-testing values near 20,000 megohms (20 gigohms), and may be unacceptable for use if insulation-resistance-testing values are below 100 megohms, regardless of whether or not the windings have surface contaminants.
http://hpac.com/motors-drives/testing-hvac-motors-0509
http://www.pearl1.org/standards/Tabl...0Electrica.pdf
http://www.ewh.ieee.org/cmte/pes/mat...t_May-08R1.pdfLast edited by nike123; 29-01-2014 at 07:39 PM.