    Leak Detection For Hotel



    We are quoting a Mitsubishi R2 VRF for a Hotel (12 rooms) and require leak detection to meet BS EN378.

    Any recommendations for this?

    Thanks in advanced.



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Leak Detection For Hotel

    Quote Originally Posted by Slim R410a View Post
    We are quoting a Mitsubishi R2 VRF for a Hotel (12 rooms) and require leak detection to meet BS EN378.

    Any recommendations for this?

    Thanks in advanced.
    Iam surprised a 12 bed vrf needs leak detection. personally we do all we can to avoid them as it's a huge cost burden. You could go tosh as they have an add on which covers this (quite expensive though)

  3. #3
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Leak Detection For Hotel

    Smallest room volume is 25m3. Total charge 25.5kg. (0.98kg/m3 for the allowed 0.44kg/m3 for R410a)

    Each en-suite will have individual extract but will probably come on with the light so cant even factor this in.

    Thanks for the info on the Tosh kit.

  4. #4
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    17

    Re: Leak Detection For Hotel

    We have used a company called murco gas detection.you could try them and get some advice .the gas detection units are installed in each bedroom and can be bit of a pain for call outs as they can shut a system off from to much hair spray etc.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Leak Detection For Hotel

    http://www.emersonclimate.com/en-US/...on_system.aspx
    dont know the cost - or if theyre any good
    Last edited by install monkey; 24-01-2014 at 10:41 PM. Reason: just put a candle in the room- if theres a leak- u get phosgene- if theres a major leak,flame goes out!

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Leak Detection For Hotel

    Hi Slim.
    best to tag that section out of contract and refer to a consulting engineer, advise client accordingly, as if you get it wrong you will loose your shirt and some. Just supply and install as specified by others.

  7. #7
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Leak Detection For Hotel

    Hi
    I would look at a TQ leak sampling very simple to install as you are only running a sample airline (6mm).
    They do a 16 point unit which would suit you ideally.

    http://www.tqplc.com/refrigeration/p...gd131,-uk-/29/
    I love the smell of Ammonia in the morning!

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,713
    Rep Power
    46

    Re: Leak Detection For Hotel

    Quote Originally Posted by Slim R410a View Post
    We are quoting a Mitsubishi R2 VRF for a Hotel (12 rooms) and require leak detection to meet BS EN378.

    Any recommendations for this?

    Thanks in advanced.
    I am surprised you even need a "Fixed" leak detection system??
    As I think RB is implying.

    If this is what you mean, then you have not read EN378!


    Leak check intervals are stated for charges up to and above 30kg.

    Systems with 300kg require fixed leak detection systems.


    Check out the attached link.
    http://www.refcom.org.uk/downloads/r...l-guidance.pdf
    A confused Grizzly!

  9. #9
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Leak Detection For Hotel

    It is always a grey area when you consider duty of care. Sometime we all just look at the requirements for compliance and service regulations. If a consultant has specified on a tender my advice is just to quote "as per tender" The leak detection may be necessary due to basement rooms etc etc

    BS EN378/2000 and EN378/2007 (Final draft) Refrigeration systems and
    heat pumps – safety and environmental requirements.

    This standard is intended to minimise possible hazards to persons,
    property and the environment from refrigeration systems and refrigerants.
    I love the smell of Ammonia in the morning!

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Leak Detection For Hotel

    what has happened with chilled/hot water systems, have not noticed any reports of Hotel motel clients drowning in their beds from those AC systems.
    But we are conned along with nu-wave technowledgy, yeah right, and all the implications of it not totally understood.

  11. #11
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Leak Detection For Hotel

    Quote Originally Posted by Magoo View Post
    what has happened with chilled/hot water systems, have not noticed any reports of Hotel motel clients drowning in their beds from those AC systems.
    But we are conned along with nu-wave technowledgy, yeah right, and all the implications of it not totally understood.
    Haven't of any guests being suffocated by refrigerant either...

    a 4 pipe system is very inefficient as you need to maintain a 100% cooling and 100% heating capacity at the same time. Although with free cooling that can be reduced if properly designed.

  12. #12
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Leak Detection For Hotel

    Just to update on EN378

    There are guidelines on the maximum volume of refrigerant that could be discharged into a space without the need for a fixed refrigerant sensor, also known as “practical limits”.

    These two examples have been taken from BS EN378 part 1 and have been widely used for air conditioning application for hotel bedrooms and small office spaces.

    The values are 0.44kg/m³ for R410A, 0.33kg/m³ for R407c.

    Above these values a sensor is required.
    I love the smell of Ammonia in the morning!