Results 1 to 6 of 6
  1. #1
    Join Date
    Jan 2014
    Location
    philippines
    Age
    37
    Posts
    4
    Rep Power
    0

    Post One liquid line for Freezers and Chillers



    Is it ok to have one liquid line for both freezer cabinets and chiller cabinets? The system has a compressor rack with 2 bitzer compound compressor for the freezers, 3 single stage compressor for the chillers and 1 condenser. Suction line is one for the freezer and one for the chiller line. Is this a good design? Also what is the formula for the calculation of liquid receiver? Refrigerant is R404a or R22. Thank you in advance for the help.



  2. #2
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: One liquid line for Freezers and Chillers

    OMG - What a mess ! Is it going and achieving temperatures ?

    I guess when you say one condenser you mean one condenser with separate low & medium temp passes ?
    If Low and medium completely seperate there is some hope .

    One liquid line means they are all joined into one system ??
    Not sure what compound compressor means .
    60% of the time it works everytime.

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: One liquid line for Freezers and Chillers

    .

    It is done like that in supermarkets.

    The low temp side pump into the high side and the
    common discharge uses the same condenser receiver
    and liquid line.

    It is quite common and works if it is sized correctly.

    Your cases will need to be individually controlled with
    shut off valves and liquid solenoid valves controlling
    temp and defrosts.

    Your compressors will need to be controlled on pressure
    and control the discharge / condensing temp by sizing the
    condenser and then cycling the condenser fans.

    Good advice here http://sporlanonline.com/literature-...nal-materials/


    Regards

    Rob

    .
    Last edited by Rob White; 03-02-2014 at 12:09 AM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: One liquid line for Freezers and Chillers

    .

    Duplicate.

    .
    Last edited by Rob White; 02-02-2014 at 12:33 PM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: One liquid line for Freezers and Chillers

    Yep, we nearly always go for a dual temp pack now. Usually 2 x dual temp packs rather than 1 HT and 1 LT. This way, if a pack should go down you still have some frozen and some chiller cabinets. We also put two blowers (one off each pack) in the chiller and freezer rooms, so again if you lose a pack, you don't lose a back up room. As long as you have fan speed control on your condenser there's no problem with single condenser, receiver and liquid line.

  6. #6
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: One liquid line for Freezers and Chillers

    Yes that is more or less standard configuration in supermarkets today, saw dirst ome about 14 years ago.
    Even nowadays seeing same configuration with transcritical co2 systems here in holland.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •