    malvern's Avatar
    malvern Guest
    Post halls 2118 screw
    I have a Halls 2118 screw compressor with an oil vent to suction. Discharge gas / oil is constantly returning to the suction, there are no regulating / solenoid valves in this line only a 5/8 ball valve . The suction temp gets up to 40 deg c. I suspect this vent valve is to relieve oil from the slide to allow the screw to unload? and maybe a seal is passing. has any boby came accross this before
    Mar 2006
    Greece
    34
    Re: halls 2118 screw
    Hi Malvern, check if the unloader works properly. If it doesn't, you've probably got leakage from the slide assembly, through the seal.
    malvern's Avatar
    malvern Guest
    Hi dimitris thanks for the help.I have checked the compressor for loading / unloading and it works fine.This is an old system which i have just taken over the maintenance on I suspect it may have been operating like this for some time.
    Jun 2001
    N.Ireland
    1,630
    Quote Originally Posted by malvern
    Er 40 deg c suction, pull the side covers off and have a look in that can't be right
    Anything coming from the discharge side wouldn't be an old return from the slide cylinder, does this happen at any particular slide loading percentage???
    sounds line a balance line to stop gas pulsations at low side position, if so the slide will cover this port after the compressor loads up to an sort of decent capacity percentage.
    Let me know how it goes, I might have a look at the halls manual if yoy can give me an idea where the pipe connects.
    Kind Regards. Andy
  1. VSD on screw machines
    By Mike Hopkins in forum New Technologies
    Last Post: 20-02-2011, 12:10 AM
  2. SCREW Compressor Problem
    By lana in forum Trouble Shooting
    Last Post: 24-01-2010, 04:31 AM
  3. do u have any data on comparison of single screw and twin screw?
    By vuputuri in forum Technical Speculations
    Last Post: 22-02-2008, 03:52 PM
  4. Mono or twin screw
    By Nirmalya in forum Industrial Compressors
    Last Post: 12-09-2006, 03:19 AM
  5. screw compressor failure
    By aygul in forum Trouble Shooting
    Last Post: 09-12-2004, 09:09 AM