    P29 Sanyo fault



    Hey all, was at a p29 sanyo fault earlier. I didn't get much time to look a the outdoor as light was fading, I'm going back tomorrow.

    My compressor windings were all the same resistance: 0.7 ohms
    My HIC board had a reading of 298 between P and N on each phase of the inverter.

    Anything else I can check?

    It's a split: Spw-cr484gvh56

    Thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: P29 Sanyo fault

    you need to power down the hic board- unplug the u,v,w and + and - test resistance accross + to u,v,w then - to u,v,w then reverseleads toget more readings, all 3 sets of resistances should be the same, either continuity or infinity- ideally a analogue meter
    megger the pot to earth too

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: P29 Sanyo fault

    Is that Hic board error fault?

    If it is my advice would be to condemn it or set it on fire!!
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: P29 Sanyo fault

    P29 its error of board or compressor. Compressor try to start? Im from pad, dont have manual on him.

  5. #5
    Join Date
    Mar 2011
    Location
    Dublin
    Age
    36
    Posts
    55
    Rep Power
    14

    Re: P29 Sanyo fault

    Quote Originally Posted by install monkey View Post
    you need to power down the hic board- unplug the u,v,w and + and - test resistance accross + to u,v,w then - to u,v,w then reverseleads toget more readings, all 3 sets of resistances should be the same, either continuity or infinity- ideally a analogue meter
    megger the pot to earth too
    I'll give that a try thanks. Meant to add that I tested it yesterday and it's not down to earth,

  6. #6
    Join Date
    Mar 2011
    Location
    Dublin
    Age
    36
    Posts
    55
    Rep Power
    14

    Re: P29 Sanyo fault

    Quote Originally Posted by RusBuka View Post
    P29 its error of board or compressor. Compressor try to start? Im from pad, dont have manual on him.
    No, when I was at it the compressor didn't even try to start, that's why I think it's the compressor, I think it's locked.

  7. #7
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: P29 Sanyo fault


  8. #8
    Join Date
    Mar 2011
    Location
    Dublin
    Age
    36
    Posts
    55
    Rep Power
    14

    Re: P29 Sanyo fault

    Quote Originally Posted by RusBuka View Post
    Thanks.
    The readings from the HIC board looked good so I called the compressor. I'll update if I hear any more about the system.

  9. #9
    maxime's Avatar
    maxime Guest

    Re: P29 Sanyo fault

    Hi,
    The fault P29 can come from the CT around the line of the power supply.

    Max

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: P29 Sanyo fault

    put an inverter checker on it to proove your hic board is ok

  11. #11
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: P29 Sanyo fault

    Quote Originally Posted by install monkey View Post
    put an inverter checker on it to proove your hic board is ok
    Change them both make more money ;-)