hi oaks
Could danfoss dircalc software be use to do pipe sizing for network of rooms and evaporators? Did you done that before?
24-01-2014, 09:41 AM #2
Re: Dircalc
Sure it can, you only have to select NH3 and make sure your inputs are correct. The result is only as good as your inputs are good.
02-02-2014, 06:24 PM #3
Re: Dircalc
thks Peter
do you simulate the network of evaporators by adding up the individual capacities of evaporators on applicable branch line?
02-02-2014, 08:04 PM #4
Re: Dircalc
Indeed, select the network for each evaporator with Dircalc and each time you connect those to the main suction and liquid line, the capacity of the main lines increases each time with the capacity you just added with a single evaporator.
Finally, when adding the last evaporator, mùost close to the compressor, you will have max capacity through the lines.
I should select the main line for max 80% total evaporator capacity so that at part load you still have sufficient speed.
We always select with a pressure drop equal to 1 K over the suction line.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.