    Aug 2013
    horsham
    28
    Mitsubishi Heavy Industries E21 fault code
    Hello my fellow engineers,
    I thought I pass on the knowledge of learning what this fault code means as it's not covered by any manual.
    Working on a 2013 FDT125VF 4way cassette, this error came up if you drop down the filter panel and try and restart the unit. It will come up with this error as they have added a microswitch to throw up a E21 "Protected stop"
    manchester
    5,639
    Re: Mitsubishi Heavy Industries E21 fault code
    limit switch on the filter access door- stop the unit before droppin filter- drop the electrics cover and theres a red plug with a jumper wire- plug that onto the pcb , then you can stick your fingers in the fan
    May 2011
    Livingston
    3
    Cheers guys. I hate working on heavy ind units for the obscure fault codes amoungst other things.
    Thanks tonashp and install monkey.
    (Obviously the first thing im gunna do is stick my fingers in it ;p heavy ind know us so well)
    May 2011
    Livingston
    3
    manchester
    5,639
    i link out the switches, they used to have a lil red jumper plug , now you have to chop the cable and thru crimp it- as the quality of the limit switch isnt the best , but mhi are quite good on servicing functions, reading the comp current, thermistor values and suction press.