Gauge readings
Hi all......I have recently switched from install to service could somebody please tell me roughly what my readings should be for each refrigerant eg r410 7bar. Thank you!
-
02-02-2014, 10:32 PM #2
Re: Gauge readings
There isn't a correct pressure for a particular refrigerant, rather the pressure would correspond with the evaporating and condensing temperatures the system is running at.
These temperatures would be dependent on the load, cleanliness of the coils and filter, air flow (or water in case of a chiller), refrigerant charge level, and ambient temperatures.
You will in time get an idea what range of pressures you would expect a particular system to be running at based on experience. In the mean time study a pressure temperature chart and see how the two are linked.Mostly found in Oxfordshire, UK :)
-
02-02-2014, 11:05 PM #3
Re: Gauge readings
Hi
sounds like you have been dropped in the deep end by your boss. No short answer to your question, you should be working with a service tech.. and develop a full understanding of refrigeration systems.
-
03-02-2014, 09:36 AM #4
Re: Gauge readings
Hi, johnyaircon
Welcome to RE forums ...
Someone push you into trouble water ....but don't worry ... you are a young man and eager to learn .... the best suggestion is to search RE forums and read interesting posts ... there are plenty of them ....
for beginning you can start here ... http://www.refrigeration-engineer.co...rigeration-101
Hope this will be of some help to you ... of course we are always here for help
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.