    single and double circuit breaker !!



    hi
    here the electric is 220 volt
    usually for cable (line and neutral) we use double circuit breaker

    images (1).jpg

    but some electrician here use single circut breaker

    images.jpg

    for the line conductor

    and connect the neutral conductor without breaker
    but directly by tape

    images (2).jpg


    so what are the advantages and disadvantage of this method



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: single and double circuit breaker !!

    jointing a neutral with tape only can result in a loose connection ( a hot joint)
    in the uk we dont fuse the neutral
    the live is always fused, some american stuff has fuses on live and neutral- if the fuse blew on the neutral then the equipment would be live all the way back to the blown fuse
    a doulbe pole mcb would be best as if it tripped it would kill the equipment and prevent any back feed from occuring

  3. #3
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: single and double circuit breaker !!

    If the joint is twisted together it shouldn't overheat, but ideally it should have a connector/screwit/wirenut/maurrette over the joint to maitain the integrety of the joint.

    And yes the American gear sometimes fuses the neutral, only seen it done over here on the primary side of some reduced low voltage systems for some reason, a fellow electrician once tried to tell me it protects both legs on the primary and secondry windings. On a centre tap secondary its understandable, but I always opted for the 110v to earth/ground system. It makes fault finding a lot easier.
    Training may be finished but experience is never complete.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: single and double circuit breaker !!

    Hi
    you can get two pole breakers with levers pinned so totally isolating field circuit, also there are RCD protection single phase breakers, similar to the one in the pics. Individually switching neutral circuit is illegal here, I have come across two pole breakers and two pole contactors on 3 phase US equipment, a definite death trap.

  5. #5
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: single and double circuit breaker !!

    sorry for my broken english
    what i want to say
    220 volt single phase
    is
    here we use the breaker with hot conductor only
    but with neutral conductor we dont use breaker
    but connect it directly
    by tapes

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: single and double circuit breaker !!

    Don't excuse for your English Kefah, we're happy you post here from a country which came so sadly in the news the last years.
    It's better to installa a double pole breaker. The difference in price is very small.
    You then can isolate a faulty section completely.
    Thé most important reason for me not to tie up al the neutrals togteher is for fault finding.
    Search once for a small electrical loss with your meggar when al neutrals are tied together? Much fun
    We even install sometimes a 3rd contact aside the breaker connected to an alarm so that the user is warned a breaker is blown.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    78
    Posts
    195
    Rep Power
    17

    Re: single and double circuit breaker !!

    From an electrical protection point of view a 2-pole circuit breaker should only really be used if the supply arrangement leaves even a remote possiblity that the neutral could ever become at elevated voltage to earth. It's better to use a circuit breaker that provides early break/late make for the live and late break/early make for the neutral, this is know as an SP+N MCB which provides overload protection on the live and only isolation on the neutral.
    Last edited by Frikkie; 19-01-2014 at 09:42 AM.

  8. #8
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: single and double circuit breaker !!

    ok
    thank u all

  9. #9
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: single and double circuit breaker !!

    Quote Originally Posted by chilliwilly View Post
    If the joint is twisted together it shouldn't overheat, but ideally it should have a connector/screwit/wirenut/maurrette over the joint to maitain the integrety of the joint.

    And yes the American gear sometimes fuses the neutral, only seen it done over here on the primary side of some reduced low voltage systems for some reason, a fellow electrician once tried to tell me it protects both legs on the primary and secondry windings. On a centre tap secondary its understandable, but I always opted for the 110v to earth/ground system. It makes fault finding a lot easier.
    Just to add to my earlier quote, I forgot that the North American 240 v residential/domestic system is a supply derived from 2 phases from a 3 phase system, and doesn't use a grounded/earthed neutral to obtain 240v on domestic/residential supplies. It has a 2 legged live/hot supply with no neutral, 120 v to earth/ground, and 240v between phases If both 120v and 240v are required, then a third wire is used as a neutral, and isn't usually protected. So the fuses and circuit breakers are there to protect both phases, and not neutrals.

    Its just when they import to other countries that have a grounded/ pme'd earthed neutral to obtain 220-240v systems, it looks like they fuse the neutral. This is one of my bug bears when I see the
    CE mark on any equipment designed, manufactured, and built, outside the UK, and then imported here. It means nothing more than a licence to import into the UK without comply to British Standards
    Training may be finished but experience is never complete.

  10. #10
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: single and double circuit breaker !!

    Quote Originally Posted by chilliwilly View Post
    Just to add to my earlier quote, I forgot that the North American 240 v residential/domestic system is a supply derived from 2 phases from a 3 phase system, and doesn't use a grounded/earthed neutral to obtain 240v on domestic/residential supplies. It has a 2 legged live/hot supply with no neutral, 120 v to earth/ground, and 240v between phases If both 120v and 240v are required, then a third wire is used as a neutral, and isn't usually protected. So the fuses and circuit breakers are there to protect both phases, and not neutrals.

    Its just when they import to other countries that have a grounded/ pme'd earthed neutral to obtain 220-240v systems, it looks like they fuse the neutral. This is one of my bug bears when I see the
    CE mark on any equipment designed, manufactured, and built, outside the UK, and then imported here. It means nothing more than a licence to import into the UK without comply to British Standards
    Well said sir....it would make a lot more sense to have 240 single but that is not what we do. All our "double pole" breakers have the levers tied together. It wouldn't do to have one leg trip now, would it.
    Last edited by MikeHolm; 21-01-2014 at 02:41 AM.