Results 1 to 9 of 9
  1. #1
    Join Date
    Jul 2013
    Location
    Jordan
    Age
    35
    Posts
    20
    Rep Power
    0

    The capacity doesn't change



    Hi,

    I have a problem in sabroe compressor in capacity, the capacity doesn't change, it's zero
    How i can solve it?
    Please help me and thank.



  2. #2
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    373
    Rep Power
    18

    Re: The capacity doesn't change

    OK, Sabroe reciprocating or screw, you know more?, model, CMO, SMC, SAB, SAB-Frick ......
    And Happy New year, Josef.

  3. #3
    Join Date
    Jul 2013
    Location
    Jordan
    Age
    35
    Posts
    20
    Rep Power
    0

    Re: The capacity doesn't change

    Sorry ,it type is screw and it model is(Xjf120l0962ff)

    And alot of happy for you and other guys.

  4. #4
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    373
    Rep Power
    18

    Re: The capacity doesn't change

    Thanks for the information, have you checked the coil?, What oil pressure, discharge pressure, the number of operating hours, the oil changed? When it all well, will be a problem in the pressure relief valve to regulate, you know what I'm writing?

  5. #5
    Join Date
    Jul 2013
    Location
    Jordan
    Age
    35
    Posts
    20
    Rep Power
    0

    Re: The capacity doesn't change

    Yes,sair i will make cheack and come back.

  6. #6
    Join Date
    Jul 2013
    Location
    Jordan
    Age
    35
    Posts
    20
    Rep Power
    0

    Re: The capacity doesn't change

    Every thing you tolled me is good,
    But maybe the problem at coil, what is your ordered?

  7. #7
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    373
    Rep Power
    18

    Re: The capacity doesn't change

    Please your email.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: The capacity doesn't change

    If load solenoid coil is damaged, swap unload coil to load coil to see if it works.

    You can also manually push directional control valve center with a small punch or screwdriver.
    Try both ends as it may be jammed.

  9. #9
    Join Date
    Oct 2007
    Location
    New Zealand
    Age
    51
    Posts
    52
    Rep Power
    17

    Re: The capacity doesn't change

    What is the controller? Unisab? Quantum?. Does it really not load/unload or is it not reading at the panel? Could be a faulty pot/transmitter.
    Current draw will give it away if it is loading or not.

Posting Permissions