    Cool Room Evap Icing Up



    Hi all, hope every one is well. I recently when to a job at a supermarket which has a compressor rack system with 4 compressors. Basically everything in the supermarket runs off the same system.

    There is a cool room in there which is set to 4 degrees but it wont pull down to temperature and just sits at around 7 degrees and after about a day just ices up.
    It has two evaporators running off the one solenoid and only one of the evaps totally ices up.

    You can hear the solenoid opening and closing when you set the thermostat so that seems all fine. I changed and TXV on the evap that was icing up and now the solenoid valve. But then I set it back down to temp and it just ices up again. Could it be the TXV on the other unit? Im not sure what else to check. Fairly newbie at this game by the way. Appreciate any input!



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Cool Room Evap Icing Up

    .

    Short of refrigerant?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Cool Room Evap Icing Up

    So you checked the superheat on both evaps?
    Assuming this system also is used for freezers, does the suction pressure regulator for these evaps operate OK?
    .
    .
    .

  4. #4
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Re: Cool Room Evap Icing Up

    No it only operates for all the display cases and cool rooms, no freezers. Yeah the superheat is pretty much identical on both evaps. I know this sounds general but my company has been working on this system for about 10 years and whenever it is short on refrigerant exactly the same display case warms up first. Also everything else in the whole shop runs fine and cycles on temperature. Not a low refrigerant issue.
    Not sure if this helps but the unit that doesnt ice up builds a bit of frost from the TXV body along the distributor lines whereas the one that totally ices up only begins at the distributor line and th body doesnt ice up.

  5. #5
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    254
    Blog Entries
    4
    Rep Power
    20

    Re: Cool Room Evap Icing Up

    From the sounds of things, I question the design.

    Why have 2 evaporators, 2 TXVs and 1 liquid line solenoid. How are you controlling defrost?

    How can 1 evaporator go into a defrost while the other one stays running? It couldn't happen as you would have a call for cooling (liquid solenoid open) and a call for defrost! You would certainly ice up the coil!

    Do both evaporators defrost at the same time?

    How old is this system? Any recent changes?

    Muiltiple Evap Diagram.jpg

    This diagram shows individual thermostats for individual rooms. Your application would require individual defrost time clocks on each evaporator with 2 independent liquid line solenoids utilizing 1 thermostats.

  6. #6
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Re: Cool Room Evap Icing Up

    It doesnt have a defrost cycle on it. When it gets down to temp the fans just keep running. The problem is something is causing the room to not pull down to temperature and then the evap ices up. The ony way to defrost it is to put the temperature up so it stays cu tout on temperature. Then after I do that. I set it back to 4 degrees come back like 7 hours later, the temperature is sitting on 8 degrees or more and one of the evaps is totally iced up.

  7. #7
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Re: Cool Room Evap Icing Up

    It is also a very old system and nothing has been changed recently.

  8. #8
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Cool Room Evap Icing Up

    Think I would check door seals,dirty evaporator faulty thermostat,s sensor/bulb location could you not put a multichannel temperature recorder in to see what's going on?,maybe a load issue,I have seen baldly designed equipment work fine for years did do not think that it's worked great but now faulty.

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Cool Room Evap Icing Up

    Evaporator has to be 100% clean to eliminate poor air flow as well.
    You need to physically look at it.
    Also check charge , infiltration like above posts state.

    Then se what happens

  10. #10
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Re: Cool Room Evap Icing Up

    Cheers guys, am going back in the morning to suss it out. definetely have a couple more things to check now. One quick question, Is it odd for one of the evaporators to totally ice up yet the other one that is maybe 3 metres to its left to not frost up at all even though they are exactly the same and both run off the same LLS and t/stat?

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Cool Room Evap Icing Up

    2 single phase fans in 1 evaporator? Baffle between both? No? Capacitor faulty on 1 fan, 1 spinning CW, the other CCW where you think both are running fine but no flow over the coil. Feel once in front of the coil.

    Door open? No, then you should face same problems with the other one too.

    Or, the faulty one takes his liquid on top of the liquid line. But then, these problems should happened already in the past.
    Last edited by Peter_1; 12-01-2014 at 03:34 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Re: Cool Room Evap Icing Up

    Quote Originally Posted by Peter_1 View Post
    2 singel phase fans in 1 evaporator? Baffle between both? No? Capacitor faulty on 1 fan, 1 spinning CW, the other CCW where you think both are running fine but no flow over the coil. Feel once in front of the coil.

    Door open? No, then you should face same problems with the other one too.

    Or, the faulty one takes his liquid on top of the liquid line. But then, these problems should happened already in the past.
    Thanks mate. Yeah 3 single phase fans per evap. Saw them spinning but yeah I will check that to. Thanks so much for replying.

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Cool Room Evap Icing Up

    Something else to check is that the drain is clear, have seen icing problems where the condensate couldn't get away.
    Mostly found in Oxfordshire, UK :)

  14. #14
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Cool Room Evap Icing Up

    QUOTED: Not sure if this helps but the unit that doesnt ice up builds a bit of frost from the TXV body along the distributor lines whereas the one that totally ices up only begins at the distributor line and th body doesnt ice up.
    ------------------

    Iced up evaporator is carrying all the load. Room can't get to temperature so no off cycle to clear evap of frost. The other evap has valve or orifice trouble.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  15. #15
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Re: Cool Room Evap Icing Up

    Quote Originally Posted by mikeref View Post
    QUOTED: Not sure if this helps but the unit that doesnt ice up builds a bit of frost from the TXV body along the distributor lines whereas the one that totally ices up only begins at the distributor line and th body doesnt ice up.
    ------------------

    Iced up evaporator is carrying all the load. Room can't get to temperature so no off cycle to clear evap of frost. The other evap has valve or orifice trouble.
    Hit the nail on the head. I should have thought of this as I changed TXV and orifice on evap that was icing up, stupid in hindsight. Changed orifice on the other one today and bang unit hasnt missed a beat. Thanks mike and everyone else!

  16. #16
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Cool Room Evap Icing Up

    Quote Originally Posted by stoljc05 View Post
    No it only operates for all the display cases and cool rooms, no freezers. Yeah the superheat is pretty much identical on both evaps. I know this sounds general but my company has been working on this system for about 10 years and whenever it is short on refrigerant exactly the same display case warms up first. Also everything else in the whole shop runs fine and cycles on temperature. Not a low refrigerant issue.
    Not sure if this helps but the unit that doesnt ice up builds a bit of frost from the TXV body along the distributor lines whereas the one that totally ices up only begins at the distributor line and th body doesnt ice up.
    Mike refs good pickup

    So are we saying the superheat was OK but unit with little ice not performing!

    Maybe in hindsight we should have asked for air on/off on Evaps.
    Suction superheat temp reading cannot be higher than air on temp.

    I think MAgoo has stated this in the past, possibly others as we'll.
    Last edited by RANGER1; 13-01-2014 at 08:23 PM.

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Cool Room Evap Icing Up

    Problem is solced completely only with replacing the orifice? are you sure there's no moisture in the system?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Re: Cool Room Evap Icing Up

    Yes Ranger was talking to the boss about this afterwards and he suggested I should have done that. I have been qualified for about a month its all so daunting still. Well I pulled the middle out of the old orifice and it was so dirty no chance it was letting anything through.

  19. #19
    Join Date
    May 2010
    Location
    Queensland
    Posts
    36
    Rep Power
    0

    Re: Cool Room Evap Icing Up

    Superheat cannot have been the same on both Evaps... How were you checking your superheat