    Daikin brc1d52 controller



    Hi guys I am wondering if anybody has or can tell me how to get an engineers manual for the Daikin brc1d52 controller, providing a manual exists. I am looking to find out how to read the thermistor temperatures via the controller? And also clear the fault history. If anybody can help? Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin brc1d52 controller

    Register with the Daikin website and you will get access to their manuals.

    To clear the error code from the display - press test to show the error code, now press and hold the on/off button for about 10 seconds.

    To read the sensors - press and hold the test button, display change to 10, press and hold the test button again and the display should change to 40.

    40 is the error history, use the timer buttons to the left of the temp buttons to move up and down the list.

    Press temp up, display changes to 41, you now have the sensor readings.
    0 = Remote controller temperature
    1 = Unit air intake
    2 = Coil sensor

    There could be others depending on the system.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Daikin brc1d52 controller

    What's number 3 on that , I grg a reading on 3 also

  4. #4
    Join Date
    Jul 2012
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Daikin brc1d52 controller

    3 is also Coil sensor

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin brc1d52 controller

    on vrv's
    Sensor data
    0: Remote controller thermostat
    1: Suction
    2: Liquid pipe
    3: Gas pipe
    Address data
    4: Indoor unit address
    5: Outdoor unit address
    6: BS unit address
    7: Zone control address
    8: Cooling/heating batch address
    9: Demand/low noise address

  6. #6
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Daikin brc1d52 controller

    Quote Originally Posted by Brian_UK View Post
    Register with the Daikin website and you will get access to their manuals.

    To clear the error code from the display - press test to show the error code, now press and hold the on/off button for about 10 seconds.

    To read the sensors - press and hold the test button, display change to 10, press and hold the test button again and the display should change to 40.

    40 is the error history, use the timer buttons to the left of the temp buttons to move up and down the list.

    Press temp up, display changes to 41, you now have the sensor readings.
    0 = Remote controller temperature
    1 = Unit air intake
    2 = Coil sensor

    There could be others depending on the system.
    Thank you Brian. In respect to clearing the faults, do I hold test button while the controller in on or off or doesn't it matter?

  7. #7
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Daikin brc1d52 controller

    And thank you guys :-)

  8. #8
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Daikin brc1d52 controller

    And The only manuals I can find are the operation manuals

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin brc1d52 controller

    Quote Originally Posted by bigspee View Post
    Thank you Brian. In respect to clearing the faults, do I hold test button while the controller in on or off or doesn't it matter?
    No, just display the error code and hold the on/off button.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin brc1d52 controller

    Quote Originally Posted by bigspee View Post
    And The only manuals I can find are the operation manuals
    I think, to be honest, that most instructions seem to be in the unit manuals and not the RC booklets.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin brc1d52 controller

    press the test button to show the last fault then hold the on/off button to clear it
    Quote Originally Posted by bigspee View Post
    Thank you Brian. In respect to clearing the faults, do I hold test button while the controller in on or off or doesn't it matter?

Posting Permissions