    Coil freezing with 5 degree c suction?



    Hi all,

    I'm working on a small air drier that's dehydrates air for an air compressor. When there is no air flow through the drier it doesn't turn off , but has a hot gas bypass valve that comes into play if the suction drops below 3 degree c. This would prevent the coil from icing up. The only place I can measure the evap pressure is at the compressor. The hot gas bypass valve tees of the discharge line straight into the suction ( bypassing the evap ) on my first call there I found the suction running at 5c , quite superheated.but I could see frost exiting the foamed in place evap? The evap had iced and blocked the air flow generating alarms on the site. I have realised there is a leak and since recharging all is good. My question is : How can my evap ice up if my suction is running above 0c?
    I understand the that the hot gas valve would be active raising the suction and superheat but shouldn't that pressure be constant down the suction? How can I have a lower suction in the evap than at the compressor?


    The more I learn the less I know......

  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Coil freezing with 5 degree c suction?

    Curly one.

    Maybe the hot gas needs to come on a bit earlier?

    Most times I've worked on these it's a gas leak or dead compressor, patch 'em up & away they go again.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Coil freezing with 5 degree c suction?

    A differential pressure over the evaporator. Where is the hot gas injected: inlet or outlet evaporator?
    What refrigerant? R407c (glide) ?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    218
    Rep Power
    17

    Re: Coil freezing with 5 degree c suction?

    The bypass tees off discharge and then tees into suction , bypassing the evap. It tees into the suction maybe 200mm from compressor . It would have been better if the bypass was fitted just after the capillary expansion device, but the way it is configured is ok if the gas is good.
    The way it is with the 2 parallel lines , one the bypas and the other the evap should maintain a constant suction pressure regardless of the fact that the system was short? Clearly the evap had iced to the degree of icing the evap closed, ice was evident exciting the evap , after an hour defrost ( left off) the system cleared itself and ran ok for a period with a 5 c suction ( compressor) until I could see ice starting to form again leaving the evap. I then recharged and all is good. I have always considered the compressor to have the lowest suction anywhere on a system, but I'm seeing the comp at 5 c and the evap must be lower than 0c?
    Last edited by Drew; 11-01-2014 at 10:35 PM.
    The more I learn the less I know......

  5. #5
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    218
    Rep Power
    17

    Re: Coil freezing with 5 degree c suction?

    Running on r 22.
    The more I learn the less I know......

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Coil freezing with 5 degree c suction?

    Drew,

    1/ Maybe ice forms for a period below 0 deg C for awhile before hot gas comes on.
    2/. Your gauges are wrong
    3/. Mixed or wrong refrigerant charge changing saturated temp of refrigerant.
    4/. Tasmania defies the laws of physics
    5/ Make sure water drain solenoid energizes & purges water, usually on a timer.
    Last edited by RANGER1; 12-01-2014 at 09:13 PM.

  7. #7
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    218
    Rep Power
    17

    Re: Coil freezing with 5 degree c suction?

    I thinks it's number 4 . Ha ha. Thanks for your input.