Gone to a job and the compressor is hot all the time without running tried the test run but no codes and just runs for 10 seconds can anyone help
Re: Hitachi outdoor compressor hot
To do have proper power? Are you drawing locked rotor amps? Perhaps it's tripping off on the compressor overload? Is the overload auto-resetting? Your compressor may be mechanically seized! Grab a meter and an amp probe and start troubleshooting!
09-01-2014, 07:38 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
We are lucky, since there is only one Hitachi outdoor unit model in whole world!
09-01-2014, 05:48 PM #4
crankcase heater works then
10-01-2014, 07:45 PM #5
Outdoor unit series UTOPIA or SET FREE (FreeSystem) ?
install monkey he's right ! It is crankcase heater works then
For example: page135 SMGB0065 rev.0
crankcase heater ON Temp. on the top compressor less than 55 CelsiusFile0123.JPG
crankcase heater OFF Temp. on the top compressor over 60 Celsius
10-01-2014, 07:50 PM #6
i meant it sarcastically! haha
10-01-2014, 08:40 PM #7
Sarcasm? Ok!
But the heater on Hitachi ES & IVX and Set Free works - 24/7