    Bitzer Octagon compressors



    I am currently commissioning some Searle CCU recip packs.I have had some trouble with one of the Bitzer Octagon comps.When I ran the comp up for the first time it sounded tight and was pulling high amps.It is a 50/50 PWS and the windiing resistances are around 2.4 ohms on both windings.The comp dose not have a conventional oil pump but a centrifugal pick up which feeds directly to the crank.I have 420 volts between phases on both windings.As the comp is brand new and the feedback I have recieved from the supplier, that the comps are fully checked and tested that there must be some other reason for the problems I am having.I was wondering if anyone else had had any such problems with the comps.



  2. #2
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Thumbs up Re: Bitzer Octagon compressors

    8FC70.2 or 8FC60.2,and give me
    evaporating temp.
    condensing temp.
    readings by ampermeter
    R 407C or what

    Best regards,
    Renato

  3. #3
    Join Date
    Jul 2004
    Location
    england
    Age
    52
    Posts
    64
    Rep Power
    20

    Re: Bitzer Octagon compressors

    Fist step is to make sure you have oil pressure, may be running in reverse. Some compressors recip can only run one way due to the type of oil pump. Also part wind comps need a delay between each winding of 3 secs min.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    We install mostly Bitzer.

    A Bitzer can run in every direction, so the oil pump isn't an issue.

    You have PWS...have you measured the 3 lines separately and wasn't there one line which pulled more Amps then the other?
    It can be that one of the windings is turned inside the opposite way so that it's magnetic field is counteracting the other 2.
    Your resistance reading will be correct but the Amps will differ.

    Some Bitzers are limited in maximum LP, if you go over it, then Amps will be too high.

    Are all the bolds tightned well, also at the underside of the plastic connection block? Sometimes the amps are correct when measuring unloaded but as soon machine starts, the loosen contact will pull more Amps.

    You said .. both windings...is it not a 3 phase motor then?

    What type of compressor do you use? All the same type on the pack?

    Keep posting what you found ,we can learn from it.
    Last edited by Peter_1; 05-05-2006 at 09:30 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bitzer Octagon compressors

    Yeah, like peter said it looks like winding A is wired CW and winding B is wired CCW or viceversa.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    But I'm still confused about the 2 windings

    If a winding is wrong connected, then this is a factory fault because it happened inside the compressor.

    You should call your supplier because this is a warranty case and they should pay you to solve this.

    I'm working this day on an Octagon and I will have a look once if (!!!) you can change it.
    Last edited by Peter_1; 06-05-2006 at 07:31 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    Another possible cause which I searched for some hours in the rain: compressor 1 has power cable A and B (50 +50%) and compressor 2 has C and D. If B and C are interchanged, then everything works fine as long as both are running.

    As soon one stops, motor which is still running comes to half power. But the magnetic field generates a new voltage in the other non-energised winding so that you can measure a voltage on the outlet of a non-energised relay of the stopped compressor.
    Do you understand what I mean?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bitzer Octagon compressors

    No, how can there be 4 wires in a PWS. There must to be 6.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    I was talking about power cables, not wires.
    1 cable for the 1st motor, 1 cable for the 2nd motor.
    A PWS has 2 cables with each 3 wires, so 6 wires total/compressor.
    A PWS motor always has 3 windings.

    Is this more clear?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bitzer Octagon compressors

    Quote Originally Posted by Peter_1
    I was talking about power cables, not wires.
    1 cable for the 1st motor, 1 cable for the 2nd motor.
    A PWS has 2 cables with each 3 wires, so 6 wires total/compressor.
    A PWS motor always has 3 windings.

    Is this more clear?
    No, a PWS has two windings, three wires per winding.

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Bitzer Octagon compressors

    Quote Originally Posted by NoNickName
    No, a PWS has two windings, three wires per winding.

    Nick,

    Us Irish will translate

    The wiring was mixed up on the job Peter was talking about.

    It ran fine if both the compressors with the mixed wires were running together.

    But if one stopped only one set of the Part Wind was being fed on the other running compressor and the compressor overloaded.

    Kind Regards. Andy

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    Help , I have to rewire all my compressors and especially all the Bitzers I've installed the last 20 years!

    How do you connect 3 wires to 1 winding?
    A winding has 2 ends

    You can't make a rotating magnetic field with 1 winding in a 3 phase motor.

    A PW motor is basically a 3 phase motor and a second 3 phase motor winded through each other, mostly wired 50/50, sometimes 70/30.

    I give up.

    Perhaps an interesting link for some: http://www.thermagroup.com/documents/Issue2.pdf
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    And what was funny, we started up under full load, everything worked fine for at least half an hour.

    The switch cupboard was located in the basement, pack standing outside the building.

    Measured AMP's on all comp --> all lower then FLA.

    Looked around a litlle bit, went back to the switch cupboard and Comp 1 overload had tripped.

    Reset it, let it run, measured AMP--> normal.

    Have to say, we were running on an generator. So I thought, generator fault???

    Monitored it some minutes (pack under full load).

    Looked to the generator, looked around a litlle bit, went back to the switch cupboard and oeps... overload of COMP 2 was tripped.

    Reset it, measured and AMPS of COMp 1 and 2 , everything normal.

    I started raining very heavy, it was already around 10 PM, I was tired working the whole day.
    And the other day, the engineering office was coming to verify everything.

    You coudl imagine that I was really p**d of.
    Attached Images Attached Images
    Last edited by Peter_1; 06-05-2006 at 06:06 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bitzer Octagon compressors

    A winding is something different than a wound wire, peter. So a winding is a set of three wound wires, eventually 2, 4 or more poles, with 3 ends. Then the three wound wires can be connected star or delta or star star in case of PWS.
    Hope it is clear know. No need to rewire your bitzers, at least not for this reason.

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    No, it isn't clear, but never mind, I gave up already.
    I know when I have to quit.

    http://www.infolytica.com/en/coolstuff/index-dcmot.html
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  16. #16
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Bitzer Octagon compressors

    Quote Originally Posted by NoNickName
    A winding is something different than a wound wire, peter. So a winding is a set of three wound wires, eventually 2, 4 or more poles, with 3 ends. Then the three wound wires can be connected star or delta or star star in case of PWS.
    Hope it is clear know. No need to rewire your bitzers, at least not for this reason.

    The Irishman will try again

    Two compressors

    Two set of wires

    Wires mixed up from one compressor to the other

    Hope this helps

    Kind Regards. Andy

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    I see from your first post you followed my explanation.
    Perhaps not in best English but because you understood it, then it can't be that bad explained.

    Andy, what's the difference between a cable and a wire? Does a cable consists of wires?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Bitzer Octagon compressors

    Quote Originally Posted by Peter_1
    I see from your first post you followed my explanation.
    Perhaps not in best English but because you understood it, then it can't be that bad explained.

    Andy, what's the difference between a cable and a wire? Does a cable consists of wires?

    Yep the wire is the conductor or conveyor of the electric.
    The cable is a collection of one or more wires in an insulated cover

    Kind Regards. Andy

    P.S I am lucky that english is my first language, otherwise I would not understand anything

  19. #19
    Join Date
    Sep 2005
    Location
    Manila, Philippines
    Posts
    7
    Rep Power
    0

    Re: Bitzer Octagon compressors

    your problem is overcahrge during commissioning

  20. #20
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer Octagon compressors

    How can the current be high due to overcharging on a semi-hermetic Bitzer, mounted on a pack?
    Explain this once fo me because I can always learn something new.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  21. #21
    Join Date
    Jun 2002
    Location
    Mumbai, India
    Age
    66
    Posts
    25
    Rep Power
    0

    Re: Bitzer Octagon compressors

    Hi,

    We had a similar problem. While commissioning a 15 H.P. two-stage Bitzer semihermetic - the compressor would trip within a few seconds of the second winding coming on load.

    Checked the current - it was showing 154 amps. As the compressor suction and discharge pressures were not abnormal checked the wiring.

    It all boils down to a very simple solution (in fact this is the right way of cabling for part winding start which we did not know at that time) - Keep the phase sequence same from incoming cable to the Motor Control Panel right upto the compressor. A sketch is enclosed.

    In our case inside the Motor Control Panel R & Y were interchanged for one of the windings (This creates no problem with star-delta starting). Once the fault was identified and corrected all was well.
    Attached Files Attached Files

  22. #22
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Bitzer Octagon compressors

    FOR octagon series, why use part winding scheme ?
    Connect the motor terminals in star wound position & operate with DOL starter . Pls look up in the terminal box , it says , 400 V Y.

  23. #23
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Bitzer Octagon compressors

    I understood what you were saying Peter, even in 2006
    ...and she said "give it to me you big fridgie"

  24. #24
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bitzer Octagon compressors

    Despite, a PWS motor still has got 6 terminals, which are the terminations of 2 internally connected stars. 3 wires per winding, the other three plus three are connected inside the motor. Maybe this sheds some light on a 4-years old thread.

  25. #25
    Join Date
    Mar 2006
    Location
    Philippines
    Posts
    35
    Rep Power
    0

    Re: Bitzer Octagon compressors

    normally part winding motors especially bitzer is with taggings in the terminals as U1, V1, W1 (for the first winding) and U2, V2, W2 (for the second winding) and since it is a part winding there must be two contactors for each winding plus and time delay for the entry of the second winding which is normally 1 sec. there must be a set of cables with 3 wires each so all in all there will be six wires. each set of cable will go to each contactor and windings. there must be some mixed in the 2nd windings wiring if it is tripping upon start up and with high amps. If it is a DOL start which is normally with octagon it will be depending on the connection if U2, V2, W2 is bundled together then the connection is STAR and you will only have 3 wires that will connect to U1, V1, W1 if it is DELTA U1+U2, V1+V2, W1+W2 and you will also have 3 wires to connect.

  26. #26
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bitzer Octagon compressors

    Yes, kaelte, but too many people forget the basics, and arrange a lunch with a dinner with what they scrounge up.

Similar Threads

  1. Bitzer gasket
    By Renato RR in forum Fundamentals
    Replies: 5
    Last Post: 04-11-2010, 10:08 AM
  2. Bitzer s6f30 2-stage compressors
    By JONAH in forum Technical Discussions
    Replies: 25
    Last Post: 27-10-2010, 07:27 AM
  3. Bitzer compressors
    By Guy Hodgins in forum Trouble Shooting
    Replies: 1
    Last Post: 18-03-2004, 03:03 PM
  4. Compressor's volume efficiency
    By John McGru in forum Fundamentals
    Replies: 0
    Last Post: 16-02-2004, 08:44 AM
  5. Comparative compressors
    By Friobernal in forum Technical Discussions
    Replies: 7
    Last Post: 28-04-2002, 07:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •