Results 1 to 50 of 50
Hybrid View
-
11-01-2014, 03:09 PM #1
Re: R404a water cooled condensing unit with 8oC cooling water
Pressure actuated, HP connected to any HP point, valve is mounted in the outlet, not the inlet so that you have a condensor full of water.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
11-01-2014, 04:18 PM #2
Re: R404a water cooled condensing unit with 8oC cooling water
Thank for your answer. I found these valves type but still have confused for selection - too much model. I will ask Supplier
http://www.danfoss.com/BusinessAreas...369fb9f20.html
Thank for your links. From these discussion, i'm understanding my situation like an air cooled condensing unit along with low ambient temp. For this situation they often said about condensing pressure regulator on refrigerant link (danfoss KVR as reference). Should i apply both of water and refrigerant type condenser pressure regulator or only one of them ?