    Smile Fujitsu Ceiling Cassette AOT18RZAL



    Hello fellow fridgies
    Have a client with above model quite old cassette that works though wall control not communicating properly with indoor. Some functions work though refuses to switch off!
    The time setting parameter shows EE:00?
    Does it sound like a remote wired control mis match? As the wall controller looks more modern than the system? Controller no:EZ0950HSE-R
    Have spoken to Fuj Gen Aus. & parts are no longer available either indoor board + wall controller.
    Also if I cannot do any good with the present setup is a aftermarket control system feasible. The present indoor board also controls float control & onboard condensate pump too.
    I also realize that an aftermarket controller will mean rewiring the outdoor unit as well as it runs a seperate pcb which is bus connected.
    If anyone has carried out similar & wish to share that would be appreciated? There are plenty of aftermarket kits around but choosing the right one to simplify the rewiring!
    I have a full wiring diagram of both indoor outdoor units as well.
    Cheers
    MC



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Fujitsu Ceiling Cassette AOT18RZAL

    Have a read on here to see what your problem is http://airconditioningfaultcodes.blo...ror-codes.html

    EE:00 - High pressure problem

  3. #3
    Join Date
    Aug 2009
    Location
    Downunder
    Age
    56
    Posts
    40
    Rep Power
    0

    Re: Fujitsu Ceiling Cassette AOT18RZAL

    Quote Originally Posted by frank View Post
    Have a read on here to see what your problem is http://airconditioningfaultcodes.blo...ror-codes.html

    EE:00 - High pressure problem
    Thanks Frank
    Though doubt it's head press problem as the system works perfect, I don't think these units have pressure switches in outdoors only temp detectors! Unless one of the thermistors are crook?

  4. #4
    Join Date
    Aug 2009
    Location
    Downunder
    Age
    56
    Posts
    40
    Rep Power
    0

    Re: Fujitsu Ceiling Cassette AOT18RZAL

    btw Frank how can we open that link without all the popup adds?

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Fujitsu Ceiling Cassette AOT18RZAL

    Quote Originally Posted by Mavricks Choice View Post
    btw Frank how can we open that link without all the popup adds?
    As it's not my site, I can only advise you to look at your pop-up blocker settings

  6. #6
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu Ceiling Cassette AOT18RZAL

    Mavricks Choice
    You started in the right way but specify model name of the indoor unit.
    E00 it's communication error between indoor unit and wired remocon.
    Necessary to understand the compatibility of indoor unit and wired remocon.
    Another option is failure PCB of the indoor unit.
    You need to check for a faulty the safety circuits of remocon communication.
    Something like L2. L3, L4 on CN17 (connector for remocon).
    CN17.png
    Last edited by bigor_2; 10-01-2014 at 07:45 AM.