    Question Chillers



    Chillers?

    What is the best?

    R717
    R290
    R1270
    R22
    R404a
    R407c
    R410a
    ect

    plate
    shell/tube
    shell/plate
    ect



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Chillers

    First one from both group

    Definitely
    Last edited by Josip; 11-03-2006 at 12:26 AM. Reason: second row

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    807
    Rep Power
    20

    Re: Chillers

    Quote Originally Posted by Josip
    First one from both group

    Definitely
    Based on what?

    Most chiller are R22+shell tube
    KasperDK,what the spec for the best?


    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    Ammonia for the low mass flow and very high latent heat and good physical properties.

    AND,

    A plate heat exchanger. Low refrigerant charge required, higher heat transfer per unit of heat transfer surface, and smaller size and lower costs.

    These should work well for the majority of the applications.

  5. #5
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    48
    Posts
    24
    Rep Power
    0

    Re: Chillers

    last year installed a Shell/plate(condenser and evap.) ammonia chiller with hp float vavle, with sabroe smc 106mk.4, Vacon Inverter(VLT), ca. 500kW at 6/12C
    cond.40C with only 13 kg of ammonia!!!!

    And in my new job iam installing 180 kw og R290 chiller plate/plate,this can be put together to produce more with 6 kg of propane(R290) no olie problems,no service problems,

  6. #6
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    48
    Posts
    24
    Rep Power
    0

    Re: Chillers

    are you using Freecooling wenn the temp outside is under the temp of the chiller water, iam servicing a systemther produce ca. 2 mW 14/10C water outer temp -3C

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Chillers

    Hello KasperDk,

    please come with some more details like piping diagram, description...

    Thanks

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    Hi kasperDK,

    are you using Free cooling when the temp outside is under the temp of the chiller water, i am servicing a system ther produce ca. 2 mW 14/10C water outer temp -3C
    This sounds like the chiller is being used as a thermosyphon with the outdoor air temperature as the heat sink.

    A very good idea. I have proposed this several times for various applications.

  9. #9
    Join Date
    Mar 2006
    Location
    Greece
    Posts
    34
    Rep Power
    0

    Re: Chillers

    410 plate,proper D.P on heat exchanger

  10. #10
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Hi all

    I am tending to go for Plate and Shell both on Evaporator and Condenser. Sabroe now build a package where the evaporator is the a plate and shell, which is also the surge vessel. The condenser is a Plate and shell also with the oil separator and the HP float built into the Plate and Shell. With Ammonia Refrigerant.

    There is nothing wrong withShell and tube heat exchangers, they have less pressure drop, but the refrigerant charge goes up along with the size

    R22 was a good refrigerant, but we can't use it in new plant

    R404a would be next best, but it pays to check R134a as it can be more effecient in some cases


    What abot the Turbocor option, R134a with very high COP's at part load, which is the majority of the year

    Kind Regards. Andy

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    What about the Turbocor option, R134a with very high COP's at part load
    Is this better than a recip. compressor?? A recip. is almost linear for part load power and capacity.

  12. #12
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    48
    Posts
    24
    Rep Power
    0

    Re: Chillers

    Quote Originally Posted by Andy
    Hi all

    I am tending to go for Plate and Shell both on Evaporator and Condenser. Sabroe now build a package where the evaporator is the a plate and shell, which is also the surge vessel. The condenser is a Plate and shell also with the oil separator and the HP float built into the Plate and Shell. With Ammonia Refrigerant.

    Hi andy

    This is the unit or Chillpac for sabroe i have installed in denmark, its a super concept and works OK


    Andy what corp. are you working for?

    KasperDK

  13. #13
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Chillers

    I like the spray chillers, range from 300 - 1100 Kw with a charge of 3 - 6 bottles of NH3.

    the tubes are not submerged in refrigerant, rather the refrigerant is pumped from the lower drum and sprayed over the tubes via several nozzles mounted on two pipes running side by side over the tubes.

    we also use plate exchangers as a condenser on these units.

    -Cheers-

    Tycho

  14. #14
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: Chillers

    I also like the spray chiller design. A company i was with designed and sold spray chill comopnents for others to complete. The ability to approach 32 degree f water without the problem of freeze up is a very popular design, espically in food processing.

    We also sold plate and shell chillers but have pulled back from these units in the large sizes. There seems to be some thermo shock problems causing leaks in the large units

    The unit design and concept is excellent just a few tech problems espically with flooded ammonia.

  15. #15
    rbartlett's Avatar
    rbartlett Guest

    Re: Chillers

    good to see you here bruce

    tell us about yourself...

    cheers

    richard

  16. #16
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by kasperDK
    Hi andy



    Andy what corp. are you working for?

    KasperDK
    Large Independant company.

    www.crossref.com

    Not a corporation big firms have plenty of room for idiots, generally in abundance

    Kind Regards. Andy

  17. #17
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: Chillers

    hi richard

    nice of you to inquire about me.
    I am doing consulting on cold storage facilities and a few ice plants had a design build contracting company for many years in the us. Use to be a sales engineer for frick before they were controlled by york, and who knows who

    Some what of an expert in freezing and blast freezing, and system design for large and small facilities.

    Also worked for a specilaty heat exchanger company, enhanced surface exchangers with a specialty towards ammonia to a fluid. Lots of titanium designs for brine .

    thanks again, hope i can be of help....
    david bruceboldy usa

  18. #18
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    Spray Chillers...

    Can anyone provide some links for review information? I would be interested in seeing some of the design criteria, GPM/sq. ft., nozzle types, and heat transfer rates.

    Thanks.

    David, can you send me an email with contact information please? It appears you and I are doing similar work. It would be nice to talk to you and share some stories.

    Best Regards,
    US Iceman

  19. #19
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    807
    Rep Power
    20

    Re: Chillers

    Quote Originally Posted by Tycho
    I like the spray chillers, range from 300 - 1100 Kw with a charge of 3 - 6 bottles of NH3.

    the tubes are not submerged in refrigerant, rather the refrigerant is pumped from the lower drum and sprayed over the tubes via several nozzles mounted on two pipes running side by side over the tubes.

    we also use plate exchangers as a condenser on these units.

    what type compressor? looks like centrifugal one
    I hear...I forget;I see...I remember;I do...I understand

  20. #20
    Join Date
    Mar 2006
    Location
    US
    Posts
    13
    Rep Power
    0

    Re: Chillers

    Quote Originally Posted by Andy
    Hi all

    I am tending to go for Plate and Shell both on Evaporator and Condenser. Sabroe now build a package where the evaporator is the a plate and shell, which is also the surge vessel. The condenser is a Plate and shell also with the oil separator and the HP float built into the Plate and Shell. With Ammonia Refrigerant.

    There is nothing wrong withShell and tube heat exchangers, they have less pressure drop, but the refrigerant charge goes up along with the size

    R22 was a good refrigerant, but we can't use it in new plant

    R404a would be next best, but it pays to check R134a as it can be more effecient in some cases


    What abot the Turbocor option, R134a with very high COP's at part load, which is the majority of the year

    Kind Regards. Andy

    well I am new guy but 134a with wmc is the only way to go for the smalller chillers 110-300ton but dual with 134a

    but i am slightly bias
    McQuay, ABB, Pool Pak, Ebtron, ArticChill, ETI, Governair, Venmar, Ventrol, Grundflos, Diakin, Reznor, Sterling, Trox

  21. #21
    Join Date
    Mar 2006
    Location
    US
    Posts
    13
    Rep Power
    0

    Re: Chillers

    Quote Originally Posted by US Iceman
    Is this better than a recip. compressor?? A recip. is almost linear for part load power and capacity.

    recips are basiclly a waste now in the 100-300ton market you need to add a vfd with that to reach the IPLV of the turbo core
    McQuay, ABB, Pool Pak, Ebtron, ArticChill, ETI, Governair, Venmar, Ventrol, Grundflos, Diakin, Reznor, Sterling, Trox

  22. #22
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Chillers

    Quote Originally Posted by bruceboldy
    I also like the spray chiller design. A company i was with designed and sold spray chill comopnents for others to complete. The ability to approach 32 degree f water without the problem of freeze up is a very popular design, espically in food processing.

    We also sold plate and shell chillers but have pulled back from these units in the large sizes. There seems to be some thermo shock problems causing leaks in the large units

    The unit design and concept is excellent just a few tech problems espically with flooded ammonia.

    We take seawater down to 28.9 F

    Maybe you worked for the company we are gonna start buying or spraychillers from, it's located in Texas.

    cant remember the name, but they have a new kind, with an allow they call Titek (or titech) where the tubes are welded to the endplates like on all steel chillers, instead of "rolled" when you have steel endplates and alloy tubes.

    -Cheers-

    Tycho

  23. #23
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Chillers

    Quote Originally Posted by lc_shi
    what type compressor? looks like centrifugal one

    It's a Howden XRV (twin screw)
    -Cheers-

    Tycho

  24. #24
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by Outside Rep
    well I am new guy but 134a with wmc is the only way to go for the smalller chillers 110-300ton but dual with 134a

    but i am slightly bias
    McQuay Rep I presume. R134a is not that popular this side of the pond, not that effecient when compared to say R404a, which would be popular. Green Peace is trying to ban all HFC refrigerants in Europe and making head way, new Fgas regulation coming in.

    Anyway it is a little hard to know which ***** to use
    At present I am using mostly R404a where possible in the ***** line.

    Kind Regards Andy.

  25. #25
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by US Iceman
    Is this better than a recip. compressor?? A recip. is almost linear for part load power and capacity.
    Apparently not

    Check the web site out.www.turbocor.com

    and decide for yourself.

    Me I am using a lot a screws and VSD's

    Kind Regards. Andy.

  26. #26
    Join Date
    Mar 2006
    Location
    US
    Posts
    13
    Rep Power
    0

    Re: Chillers

    Quote Originally Posted by Andy
    McQuay Rep I presume. R134a is not that popular this side of the pond, not that effecient when compared to say R404a, which would be popular. Green Peace is trying to ban all HFC refrigerants in Europe and making head way, new Fgas regulation coming in.

    Anyway it is a little hard to know which ***** to use
    At present I am using mostly R404a where possible in the ***** line.

    Kind Regards Andy.
    cool 404a whats that LOL yeah 134a is the new thing here 404 407 410 is only used on refigeration around here but just qouted a Airhandler with 407 since its mostly refigeration there its a abnormaly around here althought
    McQuay, ABB, Pool Pak, Ebtron, ArticChill, ETI, Governair, Venmar, Ventrol, Grundflos, Diakin, Reznor, Sterling, Trox

  27. #27
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Chillers

    404 has a very low exponent, side effect of which is the low discharge temperature, in turn leading to high oil dilution and oil transport in the system. Efficient oil separators are required, especially when coupled with twin screws. When 404a is required, I normally recommend customers with 507, or setup the chiller with extremely high SH and generous oil heaters

  28. #28
    Join Date
    Mar 2006
    Location
    US
    Posts
    13
    Rep Power
    0

    Re: Chillers

    Interesting around here the only chillers around here with those refigerents are Industrial Cooling wichs is far and few between and Ice Rinks and Ice making machines but always intrested in finding out new stuff
    McQuay, ABB, Pool Pak, Ebtron, ArticChill, ETI, Governair, Venmar, Ventrol, Grundflos, Diakin, Reznor, Sterling, Trox

  29. #29
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    There was not very much useful information on the link provided. Where energy efficiency was shown on the website, it linked to an article discussing energy reduction becoming more important. Nothing was shown to provide efficiency of this compressor.

    Quote Originally Posted by From McQuay Literature

    Energy savings with part load performance as low as 0.375 kW/ton IPLV, full load performance is as low as 0.62 kW/ton
    0.62 kW/ton is nothing to really brag about. Not bad, but not too impressive. You can get better than this with a recip. compressor with ammonia at full load.

    If you account for the utilization of all of the heat transfer surface when part load is encountered (which is what I seem to remember about IPLV ratings) the performance actually seems to improve due to the closer approached temperatures.


    Quote Originally Posted by Andy
    Apparently not
    I disagree. the literature does not seem to support the claim. Can someone provide data?

    Quote Originally Posted by Outside Rep
    ...are Industrial Cooling which is far and few between...
    Not that many because the new refrigerants are used, or, not that many you have seen?

    No doubt, the comfort cooling sector is a much larger market and more systems have been installed with the new refrigerants. But then again, not too many companies would install large ***** systems for industrial use.

    The biggest reason for large ***** systems (in industrial use) is when the use of ammonia is not politically correct or restricted due to occupancy class.

  30. #30
    Join Date
    Mar 2006
    Location
    US
    Posts
    13
    Rep Power
    0

    Re: Chillers

    The whole thing is that yes amonia is better but its not being used for comfort cooling

    also on the industrial refigeration side it is far and few between in the area I live except for the three chocolate plants that are righ down the road


    Amonia around here is very seldom used since there is not a large amount of people that know how to use it and its only used in process cooling ie chicken plants and the chocolate plants thats it

    r134a is the majority of the reffer used around here since its all basicly office space and some light industrial
    McQuay, ABB, Pool Pak, Ebtron, ArticChill, ETI, Governair, Venmar, Ventrol, Grundflos, Diakin, Reznor, Sterling, Trox

  31. #31
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by NoNickName
    404 has a very low exponent, side effect of which is the low discharge temperature, in turn leading to high oil dilution and oil transport in the system. Efficient oil separators are required, especially when coupled with twin screws. When 404a is required, I normally recommend customers with 507, or setup the chiller with extremely high SH and generous oil heaters
    You could always use a secondary colesant filter as you would in Ammonia

    High superheats damage compressors and reduce the effeciency of the compressors, not to be recomended

    507 is one people are investigating, effeciency is similar or better than R404a, maybe an answer to the chiller problem, but I still prefer what I know and what our engineers are familiar with.

    R404a is very good for screws on low temp, very small oil cooler loads, if any at all

    Kind Regards. Andy

  32. #32
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by Andy
    You could always use a secondary colesant filter as you would in Ammonia
    Been there, done that, not working. Worse of all, counter rotation while compressor stopping takes refrigerant back in the suction together with oil, which is compressed back in the discharge when it starts once again.
    Or don't start anymore and seizes for oil compression.

    Quote Originally Posted by Andy
    High superheats damage compressors and reduce the effeciency of the compressors, not to be recomended
    Your mileage may vary here. To me, SH in excess of 15°K is not an issue, as it isn't with R290 and R1270. I normally install a air to refrigerant finned coil exchanger to be installed behind the condenser coils or pipe2pipe direct transfer. Two beneficial effects: lower heat rejection in the condenser and higher SH with subsequently better refrigerant reevaporation in the oil demister.

    Quote Originally Posted by Andy
    R404a is very good for screws on low temp, very small oil cooler loads, if any at all
    Oil cooler? What oil cooler?

  33. #33
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Chillers

    Quote Originally Posted by NoNickName
    Been there, done that, not working. Worse of all, counter rotation while compressor stopping takes refrigerant back in the suction together with oil, which is compressed back in the discharge when it starts once again.
    Or don't start anymore and seizes for oil compression.
    If you have a Non-return valve on the suction line (close to the comp.), counter rotatating should not happen.


    We have colesant filters on all our units, regardless of refrigerant, never had any problems at all with them.
    do you have a line from the colesant filter section back to the compressor suction line?
    just have to ask, as I've seen those without, and the point of having one without a return to the suction quite eludes me
    -Cheers-

    Tycho

  34. #34
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by NoNickName
    Been there, done that, not working. Worse of all, counter rotation while compressor stopping takes refrigerant back in the suction together with oil, which is compressed back in the discharge when it starts once again.
    Or don't start anymore and seizes for oil compression.

    Sound like a design flaw on the unit, suction and discharge check valves needed and possibly a bleed solinoide to depressurise the compressor at off cycle



    Your mileage may vary here. To me, SH in excess of 15°K is not an issue, as it isn't with R290 and R1270. I normally install a air to refrigerant finned coil exchanger to be installed behind the condenser coils or pipe2pipe direct transfer. Two beneficial effects: lower heat rejection in the condenser and higher SH with subsequently better refrigerant reevaporation in the oil demister.
    Suction or discharge superheat, I assume discharge, finned coil would be a good point for heat recovery



    Oil cooler? What oil cooler?
    Oil coolers are often used on low temp 404a screws

    Kind Regards Andy

  35. #35
    Join Date
    Feb 2005
    Location
    Jamaica
    Posts
    121
    Rep Power
    20

    Re: Chillers

    more limitations here than even in the USA only 134a chillers used for comfort cooling like hotels there was a vilter ammonia on island but the company went out of business so its no more ,but atleast the weather is good

  36. #36
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by jamcool
    more limitations here than even in the USA only 134a chillers used for comfort cooling like hotels there was a vilter ammonia on island but the company went out of business so its no more ,but atleast the weather is good
    Can't say the weathers great here, but it is nice and green

    Kind Regrads. Andy

  37. #37
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by Andy
    Oil coolers are often used on low temp 404a screws

    Kind Regards Andy
    I know. The smilie was on purpose: no oil cooler, because it is not required, according to the compressor manufacturer literature. If I had an oil cooler, refrigeration dilution would be even worse.

    And for Tycho: no non-return valve on suction, no customer will pay for such a plus (4 inches suction pipe check valve costs an arm and a leg). And it would add pressure drop to the suction line.

  38. #38
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    Quote Originally Posted by NoNickName
    no customer will pay for such a plus (4 inches suction pipe check valve costs an arm and a leg). And it would add pressure drop to the suction line.
    The suction check valve should not be considered an optional item. The disc type check valves have low pressure drops.

    You could also use a high performance butterfly valve with a motorized actuator. On start-up the valve opens. On shutdown the valve closes. Very low pressure loss during operation.

    no oil cooler, because it is not required, according to the compressor manufacturer literature. If I had an oil cooler, refrigeration dilution would be even worse.
    I have seen some applications like this. The low specific heat ratio of some refrigerants require additional suction superheat to prevent condensing close to the compression cycle.. R-114 was similar to this also.

    In some cases you have to add a heat exchanger in the suction line to specifically superheat the suction gas.

  39. #39
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Chillers

    Thanks Iceman, I'm considering disc type check valve at the moment, and it seems it can be usable in my case.
    And you are correct for the SH thing. An air to refrigerant superheater was added in order to increase the suction temperature from -15 to +5. This is useful SH and does not affect negatively the compressor.
    Also an increased oil heater was installed to reduce refrigerant dilution at standstill.

  40. #40
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    Quote Originally Posted by NoNickName
    Also an increased oil heater was installed to reduce refrigerant dilution at standstill
    You could also insulate the oil separator and oil lines. The large surface area of the separator rejects a lot of heat you cannot afford to loose in this condition.

    Is the superheat you are adding to the suction gas coming from the refrigeration system? If the superheat comes from the ambient air, the superheat is non-useful to the net refrigeration effect. The additional superheat only helps with the oil dilution problem by keeping the oil warmer.

    And, if the superheat is non-useful it could cost you some compressor capacity due to the increase in specific volume.

  41. #41
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by US Iceman
    Is the superheat you are adding to the suction gas coming from the refrigeration system?
    Yes, it is. I wrongly wrote air to refrigerant, but it is head to back superheater

  42. #42
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    US Iceman

    You could also insulate the oil separator and oil lines. The large surface area of the separator rejects a lot of heat you cannot afford to loose in this condition.


    That would be the big one
    We took over a problem NH3 plant with all sorts of oil trips, oil heaters burning out by the arm full. Fitted the insulation and ordered trace heating, well the trace heating is still in the warehouse and the plant is a new plant

    Kind Regards. Andy

  43. #43
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by US Iceman

    Is the superheat you are adding to the suction gas coming from the refrigeration system? If the superheat comes from the ambient air, the superheat is non-useful to the net refrigeration effect. The additional superheat only helps with the oil dilution problem by keeping the oil warmer.

    And, if the superheat is non-useful it could cost you some compressor capacity due to the increase in specific volume.
    Suction liquid heat exchangers are commonly on R404a plants and are necessary in low suction superheat applications (water chillers and DX with electronic expansion valves)
    We had one plant with open recips, eating shaft seals, the manufacturer advised us to increase the superhaet settings on the electronic valves, someone did and it seemed to help. To be honest I changed the oil, realigned the compressors and set up the head pressure control, (up and down, you couldnot beleive) and oh raised the suction set point from -18deg c to -4 deg c, then the plant stopped eating seals

    Moral, proper design needed

    And proper commissioning

    As will all refrigerants

  44. #44
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    Hey Andy,

    Quote Originally Posted by Andy
    the manufacturer advised us to increase the superheat settings on the electronic valves, someone did and it seemed to help.
    This sounds like an oil dilution problem. Were the carbon faces on the shaft seal pitted and cracked?

    Also, when you changed the oil... did you change to a different type or viscosity grade?

  45. #45
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Chillers

    Quote Originally Posted by Andy
    We took over a problem NH3 plant with all sorts of oil trips, oil heaters burning out by the arm full. Fitted the insulation and ordered trace heating...
    Was the engine room temperature cool?

    I have seen several systems where a similar thing occurred due to the cool air in the engine rooms.

    One question for you. Why were the oil heaters burning out this fast? Where they not submerged in the oil sump, or bad power quality? That sounds unusual!

  46. #46
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Chillers

    Quote Originally Posted by US Iceman
    Was the engine room temperature cool?

    I have seen several systems where a similar thing occurred due to the cool air in the engine rooms.

    One question for you. Why were the oil heaters burning out this fast? Where they not submerged in the oil sump, or bad power quality? That sounds unusual!
    Engine room well ventilated, with louvres in the wall next the most of the winter weather

    Heaters burning out Sabroe MK4 163 Female drive, with an oil tank below the oil separator, basically a 6" tube below the main 24" separator, with three or four 3" vertical pipes along the 7' length joining the oil tank to the separator. One heater only Sabroe are not for saying that thee is a design fault.

    Anyway the apart from the 128 and the 163 male for rotatune (inverter speed drive) these packages are dead, having been replaced by the York corporation by Fricks

    We in fact have just insulation on one tank, with a faulty heater that is to be changed next week when the oil and filter are changed. This plant has no oil temp problems since the insulation was fitted

    You can take a look athttp://www.sabroe.com/Products/Screw...163/index.html

    Kind Regards Andy

  47. #47
    Join Date
    Mar 2006
    Location
    Lakeland
    Posts
    9
    Rep Power
    0

    Re: Chillers

    I cant really say what is the best refrigerant because centrifugal chillers are a high volume low pressure differential systems unlike rotary screw like I run which are lower volume high pressure differential system. I do know that for the years I ran centrifugal chillers R-123 was a very popular refrigerant but it is a dangerous refrigerant classified here in the U.S.A as a B-2 refrigerant

Similar Threads

  1. Absorption chillers
    By bhahmad in forum Transport
    Replies: 7
    Last Post: 31-03-2007, 04:14 AM
  2. Liquid Chillers
    By elmusasc in forum Industrial
    Replies: 2
    Last Post: 18-05-2006, 11:06 PM
  3. procedure for chillers testing......
    By drk_in in forum Fundamentals
    Replies: 2
    Last Post: 17-02-2006, 09:47 AM
  4. Chillers versus packs
    By Peter_1 in forum Technical Speculations
    Replies: 15
    Last Post: 17-01-2004, 10:48 PM
  5. Centrifugal chillers
    By reggie in forum Industrial Compressors
    Replies: 2
    Last Post: 02-05-2002, 07:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •