Results 1 to 4 of 4
  1. #1
    patriot_p's Avatar
    patriot_p Guest

    Can someone help for Soft Starter Termination



    Hi,
    Can someone help me to install this soft starter i didn't understand the wiring diagram so please check the attached image and rep me.
    Thanks
    Attached Images Attached Images



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Can someone help for Soft Starter Termination

    That wiring diagram and instructions seem plain enough, what exactly is your problem with the wiring?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    patriot_p's Avatar
    patriot_p Guest

    Re: Can someone help for Soft Starter Termination

    actually i want to know the control wiring in simple words like 220 volt on flt or st or whatever.

  4. #4
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Can someone help for Soft Starter Termination

    Functional diagram from 3 page of your booklet.
    soft starter.png
    L1,L2,L3 it is LINE.
    U, V, W it is MOTOR
    Start/Stop it is operation signal (input)
    FLT it is alarm relay (output).

    soft starter 2.png
    In real diagram you need magnetic contactor with thermal overload relay.
    Last edited by bigor_2; 31-12-2013 at 06:29 AM.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •