Results 1 to 4 of 4
-
30-12-2013, 07:18 PM #1
Can someone help for Soft Starter Termination
Hi,
Can someone help me to install this soft starter i didn't understand the wiring diagram so please check the attached image and rep me.
Thanks
-
30-12-2013, 08:42 PM #2
Re: Can someone help for Soft Starter Termination
That wiring diagram and instructions seem plain enough, what exactly is your problem with the wiring?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
31-12-2013, 03:19 AM #3
Re: Can someone help for Soft Starter Termination
actually i want to know the control wiring in simple words like 220 volt on flt or st or whatever.
-
31-12-2013, 06:01 AM #4
Re: Can someone help for Soft Starter Termination
Functional diagram from 3 page of your booklet.
soft starter.png
L1,L2,L3 it is LINE.
U, V, W it is MOTOR
Start/Stop it is operation signal (input)
FLT it is alarm relay (output).
soft starter 2.png
In real diagram you need magnetic contactor with thermal overload relay.Last edited by bigor_2; 31-12-2013 at 06:29 AM.