    Fujitsu AOT54LJBYL compressor problem



    Hi,
    I have a fujitsu AOT54LJBYL. it says the compressor cannot operate,(error code 1a, and 14 blinks/flashes on the outdoor unit).
    is there any easy way to check if it is the board or the compressor. I called for technician, he said fujitsu told him to replace both (inverter board and compressor) which is going to cost me a mint.

    I can hear that the compressor trying to start but no luck, just shuts down the whole unit with the error code mentioned above.

    The compressor is a 3 phase, I did a ohm test using just my normal multimeter and it seemed ok . not sure if I can use a normal multimeter to test the winding on a 3 phase compressor. I read somewhere that you need a special ohm meter test to do that.?

    is there a way to test if the board if it the board or the compressor itself?

    many thanks in advance,
    regards
    Misha10



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fujitsu AOT54LJBYL compressor problem

    That would depend on your electrical competence but you need to check for a balanced voltage from the inverter that supplies the power to the compressor.
    This can be done by using an inverter checker or a voltmeter but with the high voltages that are involved I personally would leave it to a professional because it can be deadly.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by marc5180 View Post
    That would depend on your electrical competence but you need to check for a balanced voltage from the inverter that supplies the power to the compressor.
    This can be done by using an inverter checker or a voltmeter but with the high voltages that are involved I personally would leave it to a professional because it can be deadly.
    many thanks Marc, will do.
    regards
    M

  4. #4
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    Ferr1a.pngerror compressor start up.pngFor handmade-diagnosis suggest Trouble Shooting #17 and #20

  5. #5
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Hi bigor_2,
    any chance that I can get a copy of the service manual/troubleshooting that you have for my unit. I found the book service manual for 18R/24r/36r which contains similar information, but would like a copy for 54L, if you dont mind.

    I have replaced the board now, it is coming up with error 17 which indicates an ipm error? not sure how to test now now?

    many thanks for replying
    regards
    Misha10

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu AOT54LJBYL compressor problem

    Evenin'

    Manual is 63MB, bit big to send and to be honest not much help either. Here's the page for the code.

    E17.pdf

    For inverter testing:http://www.refrigeration-engineer.co...verter+testing

    For this model watch out for the metal body fan motors. Yeah, said it before...Search the forum, here's a start: http://www.refrigeration-engineer.co...ighlight=ljbyl

    In your case possibly the compressor or a fan motor is seized but needs more checking to confirm.

    You don't need a special meter to test the winding resistance but you'll need a megger to test the windings to earth. Normally a fault here result in a comms error and blown fuses and PCB's.

    Good luck!
    Andy.
    Last edited by Tayters; 28-12-2013 at 09:45 PM. Reason: Added stuff.
    Health and safety first..........unless I'm in a hurry.

  7. #7
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    Below link to Service Instruction for duct type units from 18 to 54
    https://www.mediafire.com/?0fvmh7qar70ro43

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu AOT54LJBYL compressor problem

    Compressor is of DC inverter type and cannot be checked otherwise than measuring its insulation resistance with Mega-ohmmeter and comparing all 3 windings resistance with Wheatstone bridge mil-ohmmeter.
    Same goes for fan motors (BLDC type).

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu AOT54LJBYL compressor problem

    Compressor is of DC inverter type and cannot be checked otherwise than measuring its insulation resistance with Mega-ohmmeter and comparing all 3 windings resistance with Wheatstone bridge mil-ohmmeter.
    Same goes for fan motors (BLDC type).

    Or:
    http://www.refrigeration-engineer.co...p/t-20440.html
    Last edited by nike123; 29-12-2013 at 06:01 PM.

  10. #10
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by bigor_2 View Post
    Below link to Service Instruction for duct type units from 18 to 54
    https://www.mediafire.com/?0fvmh7qar70ro43

    hi,

    the link deosnt work, is there another location for the service manual.

    many thanks
    Misha

  11. #11
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by Tayters View Post
    Evenin'

    Manual is 63MB, bit big to send and to be honest not much help either. Here's the page for the code.

    E17.pdf

    For inverter testing:http://www.refrigeration-engineer.co...verter+testing

    For this model watch out for the metal body fan motors. Yeah, said it before...Search the forum, here's a start: http://www.refrigeration-engineer.co...ighlight=ljbyl

    In your case possibly the compressor or a fan motor is seized but needs more checking to confirm.

    You don't need a special meter to test the winding resistance but you'll need a megger to test the windings to earth. Normally a fault here result in a comms error and blown fuses and PCB's.

    Good luck!
    Andy.

    Thank you Andy, i found your inverter testing guide last night, very useful. I did the ohms test and voltage test using my multimeter . all tested ok. the top fan comes on, the second fan never comes on, not sure if this is due to the fact that the compressor hasnt kicked in or not, I can hear that the compressor is trying to kick in but no luck. didnt do winding to earth test as I dont have a megger just a normal multimeter.

    I changed the board, trying to eliminate that, it still didnt work, comes up with error code 17 and outdoor flashes 12 times, which indicates an IPM error. Hence I was seeking just for the service or troubleshooting section of the manual.

    I put the old board back, outdoor unit flashes 14 times. with a new board, unit flashes 12 times. all the fuses are ok and no sign of any burnt out board.

    I think the compressor on the unit is gone. I can manually turn the bottom fan on the unit by hand with easy.

    thanks for helping everyone.
    regards
    Misha

  12. #12
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    new link http://www.mediafire.com/view/kkyobi8oy9ft9xf/SI%2018_54LJBL(2).pdf
    PCB with E17 is new or used?
    Compare partN (such K04AW-****HUE-C1) on both PCB.
    Last edited by bigor_2; 30-12-2013 at 06:43 AM.

  13. #13
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by misha10 View Post
    Thank you Andy, i found your inverter testing guide last night, very useful. I did the ohms test and voltage test using my multimeter . all tested ok. the top fan comes on, the second fan never comes on, not sure if this is due to the fact that the compressor hasnt kicked in or not, I can hear that the compressor is trying to kick in but no luck. didnt do winding to earth test as I dont have a megger just a normal multimeter.

    I changed the board, trying to eliminate that, it still didnt work, comes up with error code 17 and outdoor flashes 12 times, which indicates an IPM error. Hence I was seeking just for the service or troubleshooting section of the manual.

    I put the old board back, outdoor unit flashes 14 times. with a new board, unit flashes 12 times. all the fuses are ok and no sign of any burnt out board.

    I think the compressor on the unit is gone. I can manually turn the bottom fan on the unit by hand with easy.

    thanks for helping everyone.
    regards
    Misha
    To prove the fan, power the mains off for a few minutes, swap the fan motorplugs round on the PCB and restart the system.
    Make sure system has been powered down or the high DC voltage to the fan motor will spark across the plug when you unplug damaging PCB and fan.
    Above all,remember about the metal body motors being duff.
    Worth searching the forum for using diode function to test the motor PCB.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  14. #14
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    for compressor check assemble equivalent circuit from three filament lamps (60-100 watts).

  15. #15
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by bigor_2 View Post
    new link http://www.mediafire.com/view/kkyobi8oy9ft9xf/SI%2018_54LJBL(2).pdf
    PCB with E17 is new or used?
    Compare partN (such K04AW-****HUE-C1) on both PCB.
    HI bigor_2,
    downloading the file now many thanks.

    PCB with E17 is with a new board. This board was landed to me by someone who also had the same model, he couldnt get the unit going so he bought a whole new daiken unit instead. His technician couldnt determine the problem suggest to him to buy a whole new unit. He did use the board in his system for about 20 min, but since they couldnt get it going so he pulled out the board. I was going to buy the board if it worked on my unit.

    The partN on the two boards are different:
    the new one is K08bh-****
    the old one is K04aw-******

    regards
    Misha

  16. #16
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by Tayters View Post
    To prove the fan, power the mains off for a few minutes, swap the fan motorplugs round on the PCB and restart the system.
    Make sure system has been powered down or the high DC voltage to the fan motor will spark across the plug when you unplug damaging PCB and fan.
    Above all,remember about the metal body motors being duff.
    Worth searching the forum for using diode function to test the motor PCB.

    Cheers,
    Andy.

    Thanks Andy for the suggestion.

    If it was the bottom fan, wouldnt it at least try to make a noise when it tries to start it?

    I can only hear the noise from the compressor that it is trying to start no where else.

    will try to swap the plugs around for the two fan and see if the second fan does kick in at least.

    regards
    Misha

  17. #17
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    write complete partN for both PCB

  18. #18
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by bigor_2 View Post
    for compressor check assemble equivalent circuit from three filament lamps (60-100 watts).
    Hi Bigor_2

    many thanks, will try to get someone to show me how to do this with 3 -100watts lamps.

    best regards
    Misha

  19. #19
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by bigor_2 View Post
    write complete partN for both PCB
    Hi bigor_2
    I gave the new board back. but this is what I wrote down

    new board:
    K08BH- cant read the rest
    9708016023
    edition. 01

    old board:
    K04AW-0501HUE-C1 K60602 R
    9705658035
    edition.05
    regards
    misha

  20. #20
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    Сonnect three lamps at star (Y).

  21. #21
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    [QUOTE=misha10;290382]


    Hi bigor_2
    got it. I got the numbers from the photos:

    new board:
    K08BH-K08BH-0804HUE-CI
    K38328 R
    9708016023
    edition. 01

    old board:
    K04AW-0501HUE-C1 K60602 R
    9705658035
    edition.05
    regards
    misha

  22. #22
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    Tayters's idea in the following
    one of the motors may be faulty (inside short circuit).
    for check it disconnect one of motors.
    If no effect disconnect another motor.
    before connections the power switch off for 10 minutes.

  23. #23
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    will the faulty of a fan motor make the compressor to stop working?
    inorder for the compressor to work, does the second fan need to be working at all?

  24. #24
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    one more thing that I would like to add is that, when I changed to the new board, I got the error 17 on the control panel, the outdoor unit flashes 12 times, but I didnt hear the compressor making any noise. Its like it got that error when it goes and tries to start the compressor but never got the compressor to start. no noise at all. The bottom fan never came on either.

    with the old board, I can hear that the compressor is trying to kick in making a noise but the bottom fan never came on either, then error 1A comes on and unit flashes 14 times.

    best regards
    Michael

  25. #25
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    Sorry I did not quite understand.
    My experience is that if the motor is faulty compressor is not running.
    For Tayters's idea make two situation
    1. Power switch off. Disconnect bottom fan motor. Power switch on. Start system.
    2.
    Power switch off. Disconnect upper fan motor and connect bottom fan motor. Power switch on. Start system.

  26. #26
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    Imho "new" PCB is defective with IPM error.

  27. #27
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu AOT54LJBYL compressor problem

    [QUOTE=misha10;290385]
    Quote Originally Posted by misha10 View Post


    Hi bigor_2
    got it. I got the numbers from the photos:

    new board:
    K08BH-K08BH-0804HUE-CI
    K38328 R
    9708016023
    edition. 01

    old board:
    K04AW-0501HUE-C1 K60602 R
    9705658035
    edition.05
    regards
    misha
    Newer PCB is correct substitue for original.
    K08BH-0804HUE-C1 is listed as P/N 9708013053 (yep, number on PCB is different from number you order just to make it easy...) and this number is one of the superseded part numbers from the original.

    Swapping the fan motor plugs over is to purely see if the PCB is capable of driving the fans. Remember these fan motors have a PCB inside them so diagnosing them isn't as straight forward as a normal motor.

    If you fancy a go with a meter to test the internal PCB as best you can then check here and pay respects to Mr Ozairman: http://www.refrigeration-engineer.co...ht=#post283691

    Don't forget to leave unit powered off for a few minutes before unplugging them!
    Health and safety first..........unless I'm in a hurry.

  28. #28
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    [QUOTE=Tayters;290410]
    Quote Originally Posted by misha10 View Post

    Newer PCB is correct substitue for original.
    K08BH-0804HUE-C1 is listed as P/N 9708013053 (yep, number on PCB is different from number you order just to make it easy...) and this number is one of the superseded part numbers from the original.

    Swapping the fan motor plugs over is to purely see if the PCB is capable of driving the fans. Remember these fan motors have a PCB inside them so diagnosing them isn't as straight forward as a normal motor.

    If you fancy a go with a meter to test the internal PCB as best you can then check here and pay respects to Mr Ozairman: http://www.refrigeration-engineer.co...ht=#post283691

    Don't forget to leave unit powered off for a few minutes before unplugging them!

    thanks you Andy and bigor_2,

    I did printout Mr ozairman's instruction yesterday from your previous post. thank you.

    I will try the diode test on the fan motor first, then I will swapped the fan plugs around and see if the second fan will start up.

    best regards
    Misha

  29. #29
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    Misha,
    This thread http://www.refrigeration-engineer.co...ht=#post283691 about communication error.
    In your case it's compressor or IPM.
    Remember about three lamps
    HNY!

  30. #30
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    hi bigor_2/Andy,

    i swapped swopped the fan plug, the bottom fan came on straight away. compressor made the same noise. so it is definitely the compressor now.

    got quoted $2000 just to put a new compressor in.

    thanks
    Misha

  31. #31
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    BTW, HNY bigor_2 /Andy.

    just a silly question here. I read somewhere that if the compressor seems to be seized, you just have to hit it certain spot it will start?

    how true is this, the compressor is Mitsubishi electric ANB33FCMMT. anyone worked on one of these before.

    Looks like I have look at replacing the whole system or just repairing the compressor the cost is almost the same.

    cheers
    Misha

  32. #32
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by bigor_2 View Post
    Remember about three lamps
    HNY!

    I don't think that 3 lamp test will work on DC inverter system, since DC inverter need information from compressor about position of rotor from one (inactive) winding to correctly drive compressor with other two (active) windings. Therefore, without that feedback, control circuit will stop system and show error code.

    That test is OK for AC inverters since they do not provide any feedback except current consumption.



    I personally never tried that test at DC system. With IPM error, I usually advise customer to change whole outdoor unit.
    Last edited by nike123; 01-01-2014 at 10:20 AM.

  33. #33
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by misha10 View Post
    just a silly question here. I read somewhere that if the compressor seems to be seized, you just have to hit it certain spot it will start?
    Once seized, it will quickly seize again!

  34. #34
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by misha10 View Post
    just a silly question here. I read somewhere that if the compressor seems to be seized, you just have to hit it certain spot it will start?
    It's possible for on/off compressor but not for inverter.

    Quote Originally Posted by misha10 View Post
    how true is this, the compressor is Mitsubishi electric ANB33FCMMT. anyone worked on one of these before.
    Replacement only.

    Quote Originally Posted by misha10 View Post
    Looks like I have look at replacing the whole system or just repairing the compressor the cost is almost the same.
    Replacing the whole system or outdoor.
    Last edited by bigor_2; 01-01-2014 at 02:56 PM.

  35. #35
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by bigor_2 View Post
    It's possible for on/off compressor but not for inverter.


    Replacement only.


    Replacing the whole system or outdoor.

    Replacing the whole system. appraently fujitsu doesnt sell just the outdoor unit itself. Unless I can find someone who is willing to replace my compressor. Two techinicians have said to replace the whole system so far.

    regards
    Misha

  36. #36
    Join Date
    Dec 2013
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: Fujitsu AOT54LJBYL compressor problem

    Quote Originally Posted by nike123 View Post
    I don't think that 3 lamp test will work on DC inverter system, since DC inverter need information from compressor about position of rotor from one (inactive) winding to correctly drive compressor with other two (active) windings. Therefore, without that feedback, control circuit will stop system and show error code.

    That test is OK for AC inverters since they do not provide any feedback except current consumption.



    I personally never tried that test at DC system. With IPM error, I usually advise customer to change whole outdoor unit.
    thank you very much for your valuable input Nike123.

    regards
    m