Results 1 to 3 of 3
  1. #1
    Join Date
    Dec 2013
    Location
    Australia
    Age
    43
    Posts
    2
    Rep Power
    0

    Samsung AQV24UWAN Error



    I have a 3 year old Samsung AQV24UWAN split system.

    A few days ago it turned itself off. There were 4 beeps and the Smart Saver light flashes constantly. Turning it back on, it happens almost straight away. If I leave it for half an hour, and turn it back on, it will last a few minutes and shut off again. I've tried the obvious turning off the breaker, but no luck.

    I opened the outdoor unit and found 3 diagnostic LEDs. The fault indicates "FAN ERROR". But I pulled the fan apart, and it looks fine. I can't see any evidence of bulging or leaking capacitors or any burning. Fan error could mean many things?

    Any ideas?



  2. #2
    Join Date
    Dec 2013
    Location
    Australia
    Age
    43
    Posts
    2
    Rep Power
    0

    Re: Samsung AQV24UWAN Error

    Also, should have said, the outdoor fan does spin normally. Though I noticed once or twice when I was outside and started the test mode,. the fan didn't spin until I gave it a tap. The fa isn't tight, it's as free as it can be, the bearings are fine. Could this be a capacitor issue?

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Samsung AQV24UWAN Error

    not got a manual for that, if the wiring diagram o the outdoor unit shows a capacitor for the fan then it could just be the capacitor- if you say the fan spins freely- 2 options- either use a multi meter with uf symbol for testing capacitor - (microfarads) or alternatively restart the system and slowly spin the cond fan the correct direction so after the 3 min delay if the fan starts itself going then probaby cap faulty