    Angry Lennox package unit



    I have a Lennox kha 70 with aMerit® Series Thermostat 51M32
    the unit runs ok in cooling but the 4way valve does not denergized
    on heating.
    any suggestions
    cheers



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Lennox package unit

    Faulty PCB
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Lennox package unit

    The wiring on the remote is r,b,c,g,o,y1,w1
    and the outdoor has r,c,w1,y1,g,oc,w2,y2
    R and c 24volts
    y1 cooling
    g-fan
    w1 is heating but I think it's for electric heaters
    not sure which one is for the 4way valve on heating
    cheers

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Lennox package unit

    Quote Originally Posted by ballvalve View Post
    The wiring on the remote is r,b,c,g,o,y1,w1
    and the outdoor has r,c,w1,y1,g,oc,w2,y2
    R and c 24volts
    y1 cooling
    g-fan
    w1 is heating but I think it's for electric heaters
    not sure which one is for the 4way valve on heating
    cheers

    Are you sure the model number isn't a KVHK,
    O is normally heat/cool selection I.e 4way reversing valve
    Last edited by marc5180; 20-12-2013 at 09:41 PM.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Lennox package unit

    No it's a Lennox kha 70

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Lennox package unit

    R 24v from transformer
    C common
    Y1 & Y2 cooling stages 1 & 2
    G fan motor
    W1 W2 is electric heater if fitted but sometimes O can also be for the 2nd stage electric heater.

    I can't find a copy of the wiring diagram so can't see where the 4 way valve is wired into.
    Can you not trace it back from the 4 way valve and see which terminal it comes from on the board?

    Also from the model number I would say it is a heat pump but......are you sure
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Lennox package unit

    http://www.lennoxcommercial.com/tech...ce-manuals.asp
    cant upload service manual- but its at the bottom of the list

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Lennox package unit

    http://www.mediafire.com/view/prijxcdyq93d9as/0803a.pdf
    service manual- damn mediafire had logged me out

  9. #9
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Lennox package unit

    Here is the outdoor package unit terminals .just not sure if oc is for the heating ie 4way valve
    Attached Images Attached Images

  10. #10
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Lennox package unit

    Based on document 0803a.pdf heat pump mode begins when energizes W1. See page 43. You can set a bridge between W1 and R for test WP mode.

  11. #11
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Lennox package unit

    Just looking through that manual ,reversing valve is circuit is broken when relay k8 is energised , so it must be wired through nc circuit on relay k8 ,if contacts on k8 are welded or 24 volt coil is shot reversing valve wouldnt de energise.Apologies if you already ruled this out

  12. #12
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Lennox package unit

    Also check defrost board
    The difference between genius and stupidity is that genius has its limits.

    Marc

  13. #13
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Lennox package unit

    Thermostat 51M32 is suitable for non-heat pump units. See source
    http://www.lennox.com/pdfs/manuals/Lennox_Merit_Non-Programmable_Thermostats_Manual.pdf

  14. #14
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Lennox package unit

    I was looking at the manual for the 51m32. And o is for reverse valve on heating.i was talking to a Lennox engineer and he told me to wire o on the remote to w1 on the package unit but this still didn't work.ill have a better look at unit after Christmas .just left the 4aay valve pluged off the board to let the client have heating over the holidays.