    happy christmas guys ive got a problem with the yeas sa chiller starting.the star contactor and line pull in and ct reads the amps but after a couple of seconds the delta contactor pulls in and then it drops out. With current fault. Because its reading less then 5% of the fla.is there any way of increasing the time limit of that safety. Because the chiller has full gas charge and compressors are fine. Did all simulation tests every thing runs ok electrically. Checked factory settings they are all ok.all safeties are ok. Any ideas or help would be greatly thankfull.and is there any password to change the amperage setting in the panel



  2. #2
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: york screw chiller

    Whats the type of screw compressor? Star delta must to change 0.7-1 sec.

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: york screw chiller

    Its hanbell screw. Star delta. 4 seconds change over

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: york screw chiller

    When the microprocessor initiates a start signal to run a
    compressor, it runs in star for 4 to 10 seconds
    depending upon motor current as sensed by the
    microprocessor. Normally, the transition to delta takes
    10 seconds if current is below 125% FLA. If motor
    current exceeds 125% FLA, the transition is made to
    delta after a star run time of at least 4 seconds

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

  6. #6
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: york screw chiller

    http://www.hanbell.com/en/R/TechManual/RC2-TM.pdf

    59 page

    I dont trust york, i trust IOM and SM from manufacture.
    If that manual from another compressor, find yours)

  7. #7
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: york screw chiller

    have you checked current transformer and its resistance?your starting 5% FLA measured on clamp meter or from display board.

  8. #8
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: york screw chiller

    Hi thankyou install. Rusbuka and moideen i havent checked the ct resistance but the display reads different from clamp meter the clamp meter readings are higher and i dont know how to calibrate it

  9. #9
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: york screw chiller

    Quote Originally Posted by GHAZ View Post
    Hi thankyou install. Rusbuka and moideen i havent checked the ct resistance but the display reads different from clamp meter the clamp meter readings are higher and i dont know how to calibrate it
    check the ct resistance, it is between 40-45. if there is any error,i thing the replacement of ct is the option,not calibration.

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: york screw chiller

    Ghaz.
    As far as I know and therefore could be wrong!
    But I think the display readout will never correlate with a clamp meter on a York system.
    As it is a calculation within the software.
    At least on some of the ones I have looked at in the past!
    I know there are others that will know more about this on forum.
    So hopefully they will chip in?
    Check the operation of the Auxiliary contacts on the side of the Star Delta contactors.
    Or check that your delta contacts and supplies are correct.
    I believe the software is not seeing an amperage being drawn for it to drop out the way you describe.
    Good Luck.
    Grizzly

  11. #11
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: york screw chiller

    I know more tricks, but I cant describe them. My english very bad. First of all try to push contactors by hands without power on chiller. Offen was trouble with mechanic in contactors. And one fase not connecting.

  12. #12
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: york screw chiller

    Quote Originally Posted by RusBuka View Post
    I know more tricks, but I cant describe them. My english very bad. First of all try to push contactors by hands without power on chiller. Offen was trouble with mechanic in contactors. And one fase not connecting.
    hi rusbuka, as per the first post of mr.ghaz, the FLA is only 5%.if the contactor is not proper holding it will take high amps, if the contactor auxiliary is not working it will generate transition alarm. But the display reading and actual clamp meter reading is different. So I think the CT is defective or CT wiring needs to be checked. If again the same trouble is persisting, we can think the next step.

  13. #13
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: york screw chiller

    swap ct with other circuit
    check as Rusbuka says, this is a known fault on these chillers
    also check the contactors are feeding 3 phases when pulled in, pitting will cause this fault
    is the compressor unloaded when starting?
    The history is not quick enough to record actual amps at shutdown, you need ammeter to confirm that the compressor is not tripping on too high current as well
    Mostly found in the southern part of this green and pleasant land.

  14. #14
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: york screw chiller

    Quote Originally Posted by moideen View Post
    hi rusbuka, as per the first post of mr.ghaz, the FLA is only 5%.if the contactor is not proper holding it will take high amps, if the contactor auxiliary is not working it will generate transition alarm. But the display reading and actual clamp meter reading is different. So I think the CT is defective or CT wiring needs to be checked. If again the same trouble is persisting, we can think the next step.
    Do you not read the other posts?
    Grizzly

  15. #15
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: york screw chiller

    hi guys the contactor tips are good no pitting, the auxiliarys are all ok, the wiring is good and tight,3 phases are there 415v, and 243v phase to earth.the readings on compressors is all equal ,phase rotation is ok and relay is good,liquid line s/valve is ok, the pressure equalization valves open and shut ok with no bypass or letby,