Results 1 to 4 of 4

Thread: DX System Help

  1. #1
    Join Date
    May 2008
    Location
    .
    Posts
    33
    Rep Power
    0

    DX System Help



    I need some help diagnosing a built up DX system -

    The system is running a Bitzer Semi Hermetic Compressor, liquid line splits into two seperate evaporator coils each has its own TXV and Solenoid control on the liquid line, system is running on R407c and air cooled condenser coil.

    Does one calculate super heat the same way as you would on a single TXV system?
    Oil in compressor is 'bubbling' or 'frothing' like crazy, is the best place to start diagnosis by check Super heat and Sub cooling?
    Suction Pressure is constantly hunting...

    Any advice would be appreciated.



  2. #2
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: DX System Help

    You are on the right path! Check the superheat on each evaporator, the method is always the same. You may very well have one or both TXVs flooding back slightly.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: DX System Help

    Is there a good solid supply of liquid to both TxvS?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: DX System Help

    Are there check valves at the exit of the two evaporators? Are the two evaporators running at the same temperature? (if not refrigerant can condense in the cooler one when its off and the warmer one is running.)
    Mostly found in Oxfordshire, UK :)