    Sanyo E 06 fault code ??



    Hi guys ... Got a Sanyo Vrf system , 10 indoors all with own controllers . Customer has informed me that they have workers in putting new walls in and removing other walls , one of their wall mounts needs removing , which im due to do however they have an E 06 fault on all the controllers,

    eg ...... 1- 5 E 06
    R.C No.

    Any guidance would be great as I'm due on site 2moz to investigate further .


    Cheers
    Colin



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Sanyo E 06 fault code ??

    Outdoor unit is detecting error
    signal from indoor unit.
    Error in receiving serial communication signal.
    There is an indoor unit which does not send signals when
    the power is ON.

    • E06

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Sanyo E 06 fault code ??

    check all the spurs on indoor units- ensure no ring main circuit isolated, check for cut comms cable, inspect each indoor pcb for lil red led

  4. #4
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Sanyo E 06 fault code ??

    Thanks , I'm expecting to get there and unit I'm due to move will have its power dis connected so that would explain it , fingers crossed its that simple !!

  5. #5
    Join Date
    Sep 2010
    Location
    northern ireland
    Posts
    7
    Rep Power
    0

    Re: Sanyo E 06 fault code ??

    I Had this fault a couple of weeks ago and a indoor unit was isolated at spur.