    Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1



    Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    Its a Daikin super inverter ducted outdoor unit is RZP125DV1

    I did find similar but not exact number matches.



    I need to know my air flow so I can then work out how many CFM it moves so I can re route and fix up the flex ducting.

    Possibly this number is the package deal ie outdoor and indoor, FDYP125DL

    This is an Australian model too by the way.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    From the data sheet it rated at 840 litres/sec

    http://www.daikin.com.au/home-soluti...r-conditioning

  3. #3
    Join Date
    Sep 2007
    Location
    Australia, Qld, Withcott (bottom of Toowoomba range)
    Age
    42
    Posts
    51
    Rep Power
    17

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    That is not the exact model number that I have though.....

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    The model numbers only differ by Country.

    Your unit is a size 125, so the airflow will be the same.

  5. #5
    Join Date
    Sep 2007
    Location
    Australia, Qld, Withcott (bottom of Toowoomba range)
    Age
    42
    Posts
    51
    Rep Power
    17

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    ok thanks frank

  6. #6
    Join Date
    Sep 2007
    Location
    Australia, Qld, Withcott (bottom of Toowoomba range)
    Age
    42
    Posts
    51
    Rep Power
    17

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    How do I know if my air handler is able to blow out at 840l/sec.

    I have the middle flex 400mm/16" and the one on the right that goes to the tee fitting where the smaller duct comes off. After that it is just a on/off damper.

    When I just have the main room going ie for hot hot days, I don't know if the way it is set up will allow full airflow out of the 4 supply registers. I mean we have 2x 400mm coming in from return air, but on the supply air side I have the one 400mm then the other one that is chocked down to a 250mm outlet.

    So then add in the twists and bends of the flex duct. I don't think the AC will work as best as possible like this?

    See the picture.
    Attached Images Attached Images

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    flexi ducting isnt as efficient as spiral (rigid duct)
    you want to fit volume control dampers to the 2 other ducts to increase airflow to the main occuipied room
    anemometer will give you airflow in m/sec
    then do something with the diameter of the duct-not my field

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    As the Monkey said you need a measuring device called an Anemometer.
    The basic hand held device will give you a reading of the Velocity of the air (speed) in m/s or fpm.
    Once you have the velocity reading you multiply this figure by the area of the duct to give you a volume flow.
    The formula is Volume = Area x Velocity

  9. #9
    Join Date
    Sep 2007
    Location
    Australia, Qld, Withcott (bottom of Toowoomba range)
    Age
    42
    Posts
    51
    Rep Power
    17

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    But what I am thinking is that if I know what my l/sec is, 840.

    Then I guess I need to supply 840l/s to the main area of the house. How then do I calculate how many 250mm/10" flex ducts I need to supply that much air.

    Obviously as I have 2 x 400mm return flex ducts, I could have 2 x 400mm supply ducts and then I would be right.

    But as the system sits now I have 400m down to 350 down to 300 down to 250mm etc.

    I need to find a friction chart for my flex ducts, but I do not know what brand ducting I have. I think it is similar to the Westaflex vflaex ducting. But I can't seem to find a air friction duct sizing chart for them.

    So, I wonder with my current setup if the machine is actually passing through enough air, and that the bends in the ducts and fittings etc are not bottle necking the system.

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    Doing pressure drop calculations is normally carried out during the design stage, but to do them after the system is installed you will still need to know your volume/velocity flow in each duct and for this, you will need some form of measuring device.
    The Daikin ducted fan coil will have a fan curve chart that you can plot your actual readings against to find out if it is working within it's design envelope, and this is in the Service Manual, but without actual readings you won't be able to do this.

  11. #11
    Join Date
    Sep 2007
    Location
    Australia, Qld, Withcott (bottom of Toowoomba range)
    Age
    42
    Posts
    51
    Rep Power
    17

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    Quote Originally Posted by frank View Post
    Doing pressure drop calculations is normally carried out during the design stage, but to do them after the system is installed you will still need to know your volume/velocity flow in each duct and for this, you will need some form of measuring device.
    The Daikin ducted fan coil will have a fan curve chart that you can plot your actual readings against to find out if it is working within it's design envelope, and this is in the Service Manual, but without actual readings you won't be able to do this.

    Ok, so I need to get an anemometer then?

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    I guess so.
    I don't know of any other way, but I'm up for learning

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Help trying to find air flow rate from my ac in the roof. Daiken FDYP125DLV1

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •